Siemens S7

obi wan

Member
Join Date
Aug 2009
Location
Ro
Posts
13
Hi,

I want to create a library with my personal function. Its work.
But the problem come when I use in my function a library from Siemens (for example FC40 TIM_S5TI).
When I tray to compile the library I have the errors ' TIM S5TI does not match a declaration and is not in the symbol table '. If I tray to insert FC40, the program insert a normal FC not the library from Siemens.

It is possible to resolve this problems.

Thx.
 
Not sure what you mean by "compile the library".

Anyway.
If in the project blocks window there is an FC40 block or a block with the symbolic name TIM_S5TI, then delete these blocks. Be sure to delete the symbols together with the blocks.
Then copy by FC40 from the library window to your projects blocks window. Use Ctrl-C Ctrl-V. You can then use the TIM-S5TI block in your own code.
 
S7 - problem library

I have this situation: fig 01, 02, 03. I cannot compile STL source 'ConvertToS5Time'.

And I cannot copy FC40 from library.

note: FC800 is ok because in this function I not use function from Siemens library.

01.jpg 02.jpg 03.jpg
 
Last edited:

Similar Topics

The past week we received a new piece of equipment from Germany which utilizes siemens controls. Typically in our company we use A.B. controls for...
Replies
9
Views
223
Hello I have a s7-1200 and I would like to read the tags present in this controller with my controllogix controller. The two controllers don't use...
Replies
5
Views
151
Hi need help why this “failure 5 emergency stop “ appears at every startup in the morning ? Have to shut off main switch at least 10 times on...
Replies
19
Views
308
i have two plc 1. s7-1212dc/dc/dc ip; 192.168.0.1 2. s7-1500 1513-1pn ip; 192.168.3.2 i need to get data from plc1 to plc2. any idea how to do...
Replies
5
Views
118
Hi everyone hope you'll well. Is it possible for me to download a Crack version of tia portal v13..sorry to say this but the software is very...
Replies
5
Views
199
Back
Top Bottom