Hi,

Apologies if this was already answered but i could not find it. I have downloaded a project to a tp177micro but with the wrong comms settings to the plc. My problem is that before i downloaded the project to the panel i set the startup delay to zero seconds and hence i cannot access the transfer mode of the panel to download new comms settings to the panel. I used usb/ppi cable to download project and wincc 2008. I have tried to restore to factory settings with prosave but have no .psb image to do so.

Any help on resetting to factory defaults would be greatly appreciated.

Regards,
Barry. o_O
 
Hi Barry

The images for the panel can be found under
C:\Program Files\Siemens\SIMATIC WinCC flexible\WinCC flexible Images
Sometimes Prosave is set to look in a different location.

edit: And you must use the OS Update function, and look for .img files not .psb files.
In order to connect to the panel upon powerup, activate the "reset to factory default", connect the panel to the PC, start the OS Update and then cycle power on the panel.
 
Last edited:
Jesper,

Many thanks for your quick reply. Worked a treat.

Hopefully someday i may be able to return the favour and help you.

Regards,
Barry
 

Similar Topics

Hello everyone, I've had this issue for the last 2 days where I try to assign the profisafe address to an IO block (6ES7 146-6FF00-0AB0) but when...
Replies
5
Views
123
Hello, good morning, I have been having two problems with the Tia Portal software. The first is that I have installed it on my computer and...
Replies
5
Views
157
Hello to all, I'm just starting with using CodeSys. Immediately, I have noticed that Codesys doesn't use data blocks like for example S7 does...
Replies
11
Views
172
Hi, I'm setting up a modbus master on an S7-300. It seems to work in OB1 but not when I use it in OB35. Does anyone have any ideas why? Could...
Replies
10
Views
114
The past week we received a new piece of equipment from Germany which utilizes siemens controls. Typically in our company we use A.B. controls for...
Replies
12
Views
333
Back
Top Bottom