I've configured TSEND and TRECV blocks in a S7-1511 and an S7-1214.

The 1511 CPU side looks happy and isn't reporting any errors.

The 1214 CPU side doesn't look happy. TRCV status is 80B7.

I've checked over the connection parameters as per the guidance from Siemens but cannot work out what's wrong?

Any ideas?

Screenshot attached of setup.

book1.PNG
 
You are initiating a send with a rising edge on REQ ?

Standard port is 2000. Is there a reason why you have changed one of them to 3000 ?

You are using TCP, so this should be relevant from the help for 80B7:
For system data types TCON_IP_V4 and TCON_IP_RFC:
IP address of the partner end point was set to 0.0.0.0.
Not sure why that message appears.

I probably would have chosen the sending PLC to be the active partner. Not sure if it would make any difference.
 
You are initiating a send with a rising edge on REQ ?

Yep, the REQ comes from the clock memory 1hz

Standard port is 2000. Is there a reason why you have changed one of them to 3000 ?

Originally after setting comms in the wizard, it set the 1511 port to 2000 for the send and 2001 for the recv. The port number for the 1211 stayed at 0 (presumably as it's the active partner?) Changed to 3000 to test. Port numbers are to be between 2000 and 5000 as standard.

I probably would have chosen the sending PLC to be the active partner.

There's another SEND from the 1214 and a RECV in the 1511. I might try the 1511 as the active partner and see.

I also just found this...

"TSEND_C does not support the transmission of data from boolean locations, and TRCV_C will not receive data into boolean locations."

I'm wondering if because my send/recv DB are configured as bool and the pointer directs to a bool starting range?

I'll try playing about with the DB too and just send an array over.
 

Similar Topics

Hello, I have an issue where I want to simulate an Siemens HMI panel, through NAT connection to a PLC. I have the possibility through extended...
Replies
1
Views
38
Hi all! Please inform me if i can make programing of the HMI SIEMENS IPC477D from TIA Portal software or not? I do not have WINCC software but...
Replies
0
Views
49
I have never had the pleasure of working with a "Thermistor" until now and have a question. The Thermistor is a 10KOhm 4-20mA 2-wire device and I...
Replies
4
Views
104
Hello, I have a CPU 317-2DP Firmware Version V2.1.8. In TIA Portal only V2.6 is available, and there is no option to upgrade FW. Then I open it...
Replies
9
Views
179
HI everyone, i am new to Siemens plc programming and i am in need of some help. yesterday we had an S7-1200 CPU 1214C fail to turn on an output to...
Replies
12
Views
458
Back
Top Bottom