Slc 5/01 And Opc
tafenegus
Nov 2006
oregon
Hi
I need to communicate SLC 5/01 to OPC (KEPServerEX) . This driver (kapware) does not work in a direct connection to the DH-485 port of a SLC 500 series PLC using a 1747-PIC.
What option do I have to communicate this OPC driver to this SLC 5/01 CPU
I don’t have free slot to install other communication module, if there is any
If I am going to change the CPU to SLC 5/03 or 5/04 do I need al lot of programming change?
The 5/01 only does DH485. You can talk to it through a DH+/DH485 PC card, but I am not sure if there is a Kepware driver that can do that. You may have to use RSLinx to go that route.
As for upgrading to a higher model SLC, it is very simple to do, you just select the new processor type and apply it to the project. The software will give a warning, offer to resize data tables and clear I/O, and that is all there is to it.
If the exisiting 5/01 is using the DH485 port for control or HMI purposes, that will have to be dealt with also.
You could investigate using a serial server and a device to go from DH485 to RS232. The serial server would tie onto your ethernet network and be assigned a static IP address. There would be a virtual com port assignment on your PC with Kepserver that it would use to communicate with.
Hi all, I've been making good progress with the WWTP lightning strike issue, CPU and I/O for the Plant PLC is up and running, and data is coming...
1,785
Hello I have set up a new panel view plus now I set up the OPC server to see the online tags. However I browse for tags I am getting under the...
1,741
I just updated RSLinx (Single Node) from 2.57 to 3.60 and I am having an issue pulling data in to Excel from an SLC 5/05 Previously, my...
1,348
Hello Everybody, does anyone knows how to setup AB SLC500-5 PLC communication with KEPWARE OPC using Allenbradley ethernet driver of Kepware...
5,079
H
WHAT IS The ARCHITECTURE TO CONNECT A SLC 5/04 To OPC ETHERNET 10/100Mbps? CAN I USE A INTERFACE 1761-NET-ENI SERIES C?
5,251