SLC 5/03 Output not coming on
jgar65
Jan 2006
Raleigh, NC
I had a 5/01 CPU give a CPU Fault. It lost the program and I was not able to establish communication with it. I replaced it with a 5/03 we had in stock. Had the OEM email me a copy of the program. I downloaded it and everything seems to work other than output O:4/0. I do see another output come on. I think its O4:1 but didnt make note of it. I can force the output to come on and it will work. I tried readdressing the output in the rung but still have no output. Possibly an issue when the data tables were resized when changing from a 5/01 to a 5/03?
  • PRO336R4.zip
The 5/03 scan is faster than the 5/01. Your O:4/0 is only on for one scan (B3:0/11 has an OSR). Your counter Reset pulse may be too short now for the counter to "see" it. You may need to add a timer just for the O:4/0 output in Rung 47. Don't make B3:0/11 itself last longer.
I have an strange thing happening with a SLC 5/04 On a 1746-OA16 output card I get 120 volts with or with out the output being true. The LED for...
1,852
A customer asked if I could change an output address in a SLC 500 that he thinks is bad. I've not worked with that PLC before, so I asked him to...
2,608
I just had a weird one last night and was wondering if anyone else has ever seen this. A SLC5/05, 7 slot rack. One thermocouple input, One 18...
2,112
Just looking to learn something today.... My understanding is that an output shorting on a SLC Triac card is a pretty standard card failure, with...
2,362
Experts, I have an issue with an Allen Bradley SLC-500 Output Board. The PLC is going through it ladder logic correctly and the Output terminal...
4,077