SLC 5/03 reverts back to old program

fishenguy

Member
Join Date
Nov 2007
Location
WESTERN PA
Posts
125
I have a SLC 5/03 that I made some additions to the program and downloaded it to the processor. It's been running fine for the last 3 weeks, now all of a sudden in the middle of running it reverted back to the old program that doesn't have my updates in it.
Any help would be appreciated.
Thanks and regards, Dave
 
It probably has a memory card installed it it. They can be configured to load from the memory card on power up, user initiated or on corrupt memory.

If it does in fact have a memory card, you probably need to download your latest program to the processor, then store it to the memory card. You would do this by going to Comms > EEPROM > Store to EEPROM.
 
It is very probable that an EEPROM module is installed, and you just went through a power spike that corrupted the memory and caused it to re-load.

It's likely that the conditions that caused the memory corruption have existed for a while, and that they are the reason the EEPROM was installed.

Edit: Too slow !
 
Last edited:
Just remember: To write to the EEPROM, the processor has to be in the PROGRAM MODE, it can't be in the RUN mode.
 

Similar Topics

Hello All! I am writing today because I cannot figure this out for the life of me. Another site I am affiliated with keeps having their slc 5/03s...
Replies
10
Views
182
I’m attempting to send a temperature from a SLC-5/02 to an EZiMarquee display. The vendor said to use a MSG instruction to send the data to the...
Replies
1
Views
110
Hello all. I have a few SLCs in my plant and of late we've seen a weird issue: The system will be running normally and then randomly the outputs...
Replies
2
Views
120
I am working on setting up a Prosoft Datalogger model PLX51-DLplus-232. This unit will be collecting data from a SLC 5/05 on the DB9 port set to...
Replies
3
Views
127
I have a redundant ControlLogix being set up. This program reads a value from a remote site which happens to be SLC PLC. Rockwell mentions SLC...
Replies
2
Views
111
Back
Top Bottom