SLC 5/04 and DF1 Half-Duplex Slave
jgreenewv
Aug 2002
New Mexico, USA
242
I am working on a project where the consulting engineer is requiring 3 SLC 5/04s messaging half-duplex over a phone line. I can set up the processors so one is a DF1 Polling Master and the other two are slaves, but I was curious if it is possible to run all three as slaves and still message. Thanks.
Well I tried something similar. I tried two 5/04 processors with both set as DF1 Slaves. No communications were possible. All messages timed out without a DF1 Master.
OG
You can message from slave to slave in DF1 Half-Duplex, but there still has to be a master in the system polling those slaves and proxy-handling the slave-to-slave messages.
One of your SLC's will have to be the DF1 Half-Duplex Master.
one more trick....
Note that if your SCADA is configured as a master on the network, then all 3 SLC's can be slaves. The Scada will handle the polling arbitration.
I am working on setting up a Prosoft Datalogger model PLX51-DLplus-232. This unit will be collecting data from a SLC 5/05 on the DB9 port set to...
104
Is it possible to create MSG in SLC to read data from a mircologix 1000 via serial DF1? I have Micrologix 1000 and SLC5/04, the serial port on...
1,790
Was wondering if this was possible, or if anyone has had experience with it.
1,935
I have 20 SLC 500 5/03s I want to put them on a ethernet network to Citect. I figure I will have to use use the the 1761-NET-ENI module I prefer...
2,345
Hello, I am thinking this configuration would work. SLC 5/04 Connected to a 1747-DPS1 and One port of the splitter going to a panelview via DF1...
1,540