SLC 5/05 ETH setup
mfmckenzie
Apr 2011
Tennessee
I have a slc 505 ethernet cpu that I put in to replace a bad 504 and I cannot communicate with it. I cant even get links to comm via the rs232 port. Need help please.
Did you try RSLinx Autoconfigure for the RS232 DF1?
Did you default the 5/05 processor?
Did you see if the 5/05 can be assigned an IP address with the BOOTP/DHCP utility? (Connect ONLY the computer and the 5/05 together for this to eliminate possible external DHCP servers).
Did you read the manuals for the 5/05?
If you tried Auto Config and it didn't work, ensure there is nothing else trying to use the same Comm port.
I have had issues before where Siemens is trying to use the port so Rockwell cant access it.
Mark
In addition to Mark's advice above, try connecting to an existing, working processor first with your serial cable. If that works, go back and try the auto config again. If connecting to an existing processor doesn't work, follow Mark's advice, and/or try a different cable, or a null modem adapter.
Check that there isnt a memory card with an old program.
Check that the SLC5/05 is properly reset.
If properly reset, it will show a slowly flashing FLT when powering up.
Reset it by disconnecting the battery, and shorting the big fat capacitor that sits next to the memory card slot.
I have found the problem. The jumper connector on the card was on program. I removed it and got online no problem. Now I have a comm hardware flt on my panelview 600.
Hello, how can I make a connection to ETH/IP device on SLC 5\05 processor? I know that there is EEM instruction, but unfortunatelly there isn't...
2,940
I’m attempting to send a temperature from a SLC-5/02 to an EZiMarquee display. The vendor said to use a MSG instruction to send the data to the...
90
Hello all. I have a few SLCs in my plant and of late we've seen a weird issue: The system will be running normally and then randomly the outputs...
103
I am working on setting up a Prosoft Datalogger model PLX51-DLplus-232. This unit will be collecting data from a SLC 5/05 on the DB9 port set to...
104
I have a redundant ControlLogix being set up. This program reads a value from a remote site which happens to be SLC PLC. Rockwell mentions SLC...
96