i have a 505 and a micro 1100 on the same same network.
how can i set an output on the 1100 when i have a bit to go high in the 5 05?
thank youo_O
Ideally, you would set up a MSG to read a data table (or part of a data table) from the other PLC. For instance, if you want to open a valve with the ML1100 when a bit in the SLC5/05 is high, you would read the status of the bit in the SLC5/05 and the corresponding bit in the ML1100 would be a condition for the valve output.
To make things easier to troubleshoot, I recommend using the same data table for both PLCs. Example:
Read 1 word from SLC5/05 data table N7:0 to ML1100 data table N7:0. This will read 16 bits from the SLC. If you read 2 elements, it will read 32 bits, etc.)
In order to populate the data table, you will have to re-assign the OTE bit in the SLC to an address within the data table (N7:0/0, for instance). An XIC of N7:0/0 in the ML1100 would be tied to the OTE for the valve.
You can also read "B"-type data files, and probably others. I like "N" files because i can also use them to read integer values, such as pressure, from another PLC
Hi, I have 6 SLC 5/02s on 485 network. One of the processors faulted. I've replaced it and downloaded the program into the replacement using the...
1,630
I am doing some project work in a plant with older equipment which will NOT be updated. They will buy a new line in the near future so are using...
3,977
I have a Virtualbox set up with an installation of FreeDOS 1.1 I have a SLC-150 I'm trying to communicate with via the 1745-PCC. My host machine...
1,677
Happy new year one and all. Have a project i am working on at the moment and having a bit of issues. * Have a panel view 600 talking to a...
2,217
I’m attempting to send a temperature from a SLC-5/02 to an EZiMarquee display. The vendor said to use a MSG instruction to send the data to the...
90