SLC 5 analog input problem

I edited my comment while you were typing that :)

OG

Yeah, I went back and took a second look myself.

If the OP has it configured for "Class 1" then I believe your original statement would be correct. "Class 3" has all the configuration options.
Just to confuse the OP more.
 
So, if my analog input is set to engineering units, it will use the actual value?

In my 0 to 1 volt input, set to engineering units I would use a 0 minimum and 1 maximum input on the SCP?

Ain module config.JPG
 
Last edited:
No. Look at the table Mickey posted in post #5. At the bottom of the first page there is a table titled, "Channel Data Word Values for Engineering Units".

-10.25 to +10.25 volt would be scaled as -10,250 to +10,250

Therefore -10 to +10 volt would then be -10,000 to +10,000
So then 0 to +10 volt would be 0 to +10,000

Which means 0 to 1V would range 0 to +1000

OG
 
Last edited:

Similar Topics

Hey guys, Well, the troubleshooting continues for the client who got hit by lightning. New CPU has been installed, and is working! That's the...
Replies
12
Views
3,342
In my 1746-NIO41 analog input card , for a full 20mA input , the reading shows only 16383 ,why is it so ? for input address "i:3.1"
Replies
3
Views
1,986
A unit I work on experienced a lightening strike, andthis resulted in a number of failures. However, I'm puzzled about one issue.. The unit uses...
Replies
4
Views
4,317
Dear , problem : Adding and configuring analog input module 1794-IE8 to existing running system SLC 5/03 through 1747-BSN (DH485) System: - 2...
Replies
1
Views
3,768
I'm feeling pretty stupid tonight because I can't remember process to install and set up my 1746-NI4 analog card in my SLC 500 PLC. It has been...
Replies
2
Views
3,889
Back
Top Bottom