If the OP has it configured for "Class 1" then I believe your original statement would be correct. "Class 3" has all the configuration options.
Just to confuse the OP more.
No. Look at the table Mickey posted in post #5. At the bottom of the first page there is a table titled, "Channel Data Word Values for Engineering Units".
-10.25 to +10.25 volt would be scaled as -10,250 to +10,250
Therefore -10 to +10 volt would then be -10,000 to +10,000
So then 0 to +10 volt would be 0 to +10,000