slc 500 power supply problem
medo
May 2004
hi
:) i have a slc-500 series A . my problem as following.
** our power supply source is dc battery charging with solar cells, all over the day,so at midnight plc is not connected,then when removing the power supply fuse (not burnt fuse) and install it again , the power back to plc.for now i do not know if its a low voltage problem coming from battery at night,while no sun ,or its a problem related to the power supply unit itself.and what is the effect of supply voltage on plcs modules runing.
thanks
I had to read your inquiry twice before I thought of what may help you. You may try to add a separate external timer with voltage regulator on the DC solar power. The problem MAY be that the PLC is trying to start and has a power ploblem. The timer could be set to activate the power to the PLC long after the voltage has stabilized from the solar cells. The regulator will turn off if power is low.
To test for now, turn off power to the PLC before it is low, and then turn on the power to the PLC the next day when solar/battery power is OK.
Bitmore
hi Bitmore,
thanks alot for helping me , i really feel so grateful and you helped me alot.
More details
Medo
Do you mean that when it comes midnight your plc is off (no power) and when you remove the fuse while it's midnight also the PLC be on.(power on)
There are some more details we want to know what is your PLC Power supply type? ,what is the configuration for your PLC ?and is the power supply is compatable with this configuration or not?Did you measure the voltage from your batteries when the PLC is of?What is the capacity of your Batteries(A/hour)?
Please provide this information so we can help you.
Good luck
Re: More details
hesham said:
Medo
Good luck
plc power supply proplem.
hi,
- many thanks mr Hesham being you try to help me,ijust need to inform you ,we have already overcome our PLC power supply problem,by changing the old batteries by new,this after we had found much drop in batteries voltage by measuring it at the time of the problem,so the problem no loger occur since we have changed the batteries.
best wishes ,mr Hesham.
keep in toutch.
your friend Medo.
If I were to download a program that had a tag called "Count" that had an initial value of zero, and I MOVed the value of a counter accumulator...
2,058
Hello there, I am new to your site so please excuss the inexperience. I have a SLC 5/04 that loses its program everytime we cycle power on it...
43
24,840
does anyone know where you can purchase a power supply for a 1747-L30B fixed hardware processor?
2,437
Hi, Just one question about SLC500 memory. Few days ago I had long power loss in a plant and my PLCs were ofline for almost 1 hour. When a...
3,810
I had a question about the +24 VDC output in the SlC 500 Power Supply ( 1746-P4 ). What is the purpose of this output? Can I use this output to...
4,539