SLC5 to ControlLogix DH+ communications
wa5yom
Sep 2003
Ardmore, Oklahoma
138
I have a SLC504 to SLC504 application running.
SLC504 #1 has read and write MSG blocks that simply read and write data from "N" files resideing in SLC504 #2.
SLC504 #2 has no ladder logic it just holds the data for SLC504 #1.
I am replacing SLC504 #2 with a ControlLogix PLC.
I can see both devices over the Network. All DH+ addresses are correct and the ControlLogix DHRIO module is set to default settings, which is correct since there is no remote network and the processor is in slot 0.
When I execute the MSG Read I get the following error:
"Illegal address, address does not exist, or does not point to something usable by this computer"
The best I can tell is that the error is referring to the "N" file in the ControlLogix processor.
The file does exist and appears to be configured properly.
I have to be missing somethin easy here.
Any thoughts?
Thanks,
Tim
You can use messaging from SLC#1.
Be sure that you have the mapping table set up.
This can be found under Logic, Map PLC/SLC messages tree.
It is mapped accordingly..
File Number 200
Tag Name N200
Basicaly I am reading N200 from the CLX and placing it in the cooresponding N200 file in the SLC.
By doing so I have changed the error message to the following.
"Local processor detects illegal file type"
You say the processor is in slot 0, and the DH+ RIO card is on default settings, which I think is also slot 0, until you map it using LINX.
I went down this road last year.
I have the DHRIO card configured properly as slot 2...
Interesting....when I read the CLX manual it said that "N" files coorespond to DINT file in CLX....
I've never actually done any SLC to CLX communication, but have done quite a bit with PLC5 and CLX over DH+. In that situation, the CLX tags have to be type INT. I'm assuming (I know, not a good thing to do) that the SLC will behave the same.
That got it.....Thanks for all the help everyone.
Interesting hopw the manual says that the N file is a DINT file in CLX...but I still had to make a a INT file to work...
Tim
Which manual are you citing ? I'd like to see if it's incorrect or out of date.
I have always created ControlLogix INT[x] arrays and mapped them to SLC/PLC data files in order to allow PLC-5 and SLC-500 controllers to access data in the ControlLogix.
I am trying to figure out how to send messages over ethernet to a SLC5/04 from a 1769-L32E (and vise versa) using the Digi One IAP. I am pretty...
2,942
Using a message box in ControlLogix to read from a SLC5/04 on DH+. The correct tag is being read, but the wrong info is coming through. I should...
2,380
I have SLC5/05 with ethernet port and want to communciate with a controllogix in 17 rack via seperately ethernt card Enet. In Controllogix I want...
6,759
Good day to you all and congrats to great job done hear !! I try to find something mentioned for the above "title" but i cannot. For a recent...
7,703
I have wasted a week trying to figure out how to connect an SLC5/03 with my laptop. I do not have and can not Buy the 1747 UIC and PC3 cables. I...
2,584