Slightly OT: 24V brake contactor selection
Ken Roach
Apr 2002
Seattle, WA
17,480
I need a little sanity check and hopefully advice from some experienced users.
I have a mechanism that we're driving with a JVL MAC3000 integrated servo motor. It has a nice ProfiNet interface to an S7-1500, and the MAC00-EP4 network daughtercard includes a network-controllable or servo-controllable output, but it can only supply 15 mA.
I also have to provide a brake on one of the stubs of the gearbox we're driving. Our mechanical designers have selected one with a 24V brake coil. The only other technical information is that the coil resistance is 30 ohms.
https://www.mikipulley-us.com/bxr-16-10-p-30.html
OK, I=V/R so it will pull about 0.8 A. I know I need a DC snubber in parallel with the brake coil.
What sort of relay or contactor is appropriate for switching an inductive DC load like this ? Could I use a tiny 700-HL solid state terminal block relay, since it says it has a DC rating of 2.0 A ?
If this isn't mission critical and you can live with a slower brake set time I would feel comfortable with the 700-HL solution. Just make sure you have a diode across the brake coil and I think you will be good.
Keith
They don't say is the coil voltage is 24VAC or 24VDC
I don't know why they don't say but I would assume it's DC
if it's DC then you just need a flyback diode across the coil. It will limit the collapsing field voltage to less than 1 V, I use them all the time
as for the supplying the power you just need a 2 amp or higher rated relay
Ken,
we use a lot of servos with brakes. they go up/down or in/out.
what we have is the drive power connected to a reversing motor starter rated for the job with with a set of auxiliary contacts powering the brake module.
Seimens and Allen Bradley with no issues. sorry, someone cut a cable on the production line, gotta run.
hope this helps, james
I have been tinkering with a little DIY remote access stuff lately, prompted by some recommendations and challenges on this forum. To my...
1,839
Looking for an economic way to monitor kWh and kVARh on multiple circuits (up to 10) in a single distribution board. The Square D Power Logic...
1,709
Does anyone make a "positioning cylinder" like the Festo DDPC but with a digital encoder feedback ? I have an application where a 0.0005 mm...
1,765
This is a little OT, but I would like some general input. I have an machine control cabinet with an HMI as well as numerous standalone LED-bulb...
6,535
How do I calculate wire and breaker size for 2 motors starting simultaneously? Thanks
2,379