I need a little sanity check and hopefully advice from some experienced users.
I have a mechanism that we're driving with a JVL MAC3000 integrated servo motor. It has a nice ProfiNet interface to an S7-1500, and the MAC00-EP4 network daughtercard includes a network-controllable or servo-controllable output, but it can only supply 15 mA.
I also have to provide a brake on one of the stubs of the gearbox we're driving. Our mechanical designers have selected one with a 24V brake coil. The only other technical information is that the coil resistance is 30 ohms.
https://www.mikipulley-us.com/bxr-16-10-p-30.html
OK, I=V/R so it will pull about 0.8 A. I know I need a DC snubber in parallel with the brake coil.
What sort of relay or contactor is appropriate for switching an inductive DC load like this ? Could I use a tiny 700-HL solid state terminal block relay, since it says it has a DC rating of 2.0 A ?
I have a mechanism that we're driving with a JVL MAC3000 integrated servo motor. It has a nice ProfiNet interface to an S7-1500, and the MAC00-EP4 network daughtercard includes a network-controllable or servo-controllable output, but it can only supply 15 mA.
I also have to provide a brake on one of the stubs of the gearbox we're driving. Our mechanical designers have selected one with a 24V brake coil. The only other technical information is that the coil resistance is 30 ohms.
https://www.mikipulley-us.com/bxr-16-10-p-30.html
OK, I=V/R so it will pull about 0.8 A. I know I need a DC snubber in parallel with the brake coil.
What sort of relay or contactor is appropriate for switching an inductive DC load like this ? Could I use a tiny 700-HL solid state terminal block relay, since it says it has a DC rating of 2.0 A ?