SNPX Protocol for Magelis
gdoel
Apr 2004
Does anyone know where I can download the SNPX protocol for a Magelis OIU. I need to program the Magelis to work with a GE 9030 PLC and need the SNPX protocol.
Schneider Electric sells a CD with third part party protocols, part #XBTL1PROT.
This CD contains: Siemens AS511/3964R, PPI, MP1; Omron SYSMACWAY; GE Fanuc SNPX; and AB DF1, DH485.
Depending on how you're communicating with the 90-30, you might be able to use Modbus. I'm assuming Modbus is the native protocol of the Magelis line, dangerous as that assumption might be. Either of the ports on a CMM311 module can be configured as Modbus slaves as can the serial ports on a CPU351 or CPU363.
Modbus can only directly access %I, %Q, %AI, and %R memory in the 90-30. If you need to display data from other types (%M for example), you'll need to add ladder logic to copy the data to one of those four types.
Hello, I have a Ge Fanuc 90-30 system with a Cutler Hammer PM 3000 Power series HMI. Besides the HMI, the customer is happy with the controls side...
1,029
Hello All A question to the forum I need to interface to a GE controller. I understand that the PE serial protocol is called SNPX I wonder if...
3,443
Dear all, I want a communication between pc and fx5u. I am considering SLMP protocol. I think it is well documented. But many of the third party...
121
Hi all Trying to remotely connect to a TIA Portal PLC. I can ping it without a problem but can't get my software to connect. I've opened port...
361
I’m working on getting a Parallel Redundancy Protocol PRP system set up in a lab situation. The L73 PLC is in rack 4. 3 io racks are 1,2,3. I...
777