Hi guys,
I am in need of some advice from people with experience with the above.
I am currently replacing a client's SST-PFB-CLX profibus scanner card with an SST-PB3-CLX as part of a full control system upgrde project. The original i/o configuration is not available on the engineering pc and I have tried 2 options to acquire and download the i/o configuration to the new card, neither successful.
I installed the SST Profibus configuration tool on the engineering pc and I tried searching for the PA devices on the network using the new SST card but only found 2 instruments out of 100 using both the ethernet option and RSLinx option. I have tried all baud rates but I knew beforehand 93.75 kbps was the correct option from the segment coupler manual.
I also tried connecting the SST Profibus configuration tool to the existing SST card to upload the existing i/o configuration without success. The manual says it is possible but I cannot get it to work. If I use the RSLinx option in the configuration tool I get an error 'opening rslinx connection to TCP-1 failed'. RSLinx Gateway is installed on the engineering pc. If I select the ethernet option in the configuration tool I get an error 'failed to read module id'.
How do I get the i/o configuration from the existing card or create a new i/o configuration by searching for new devices?
The card is on the plc rack. The plc is AB v30.011. RSLogix v30. RSLinx GAteway v3.9. All instruments are E&H PA using Pepperl Fuchs segment coupler. Connection from pc to plc is via ENET module on the plc rack.
I am in need of some advice from people with experience with the above.
I am currently replacing a client's SST-PFB-CLX profibus scanner card with an SST-PB3-CLX as part of a full control system upgrde project. The original i/o configuration is not available on the engineering pc and I have tried 2 options to acquire and download the i/o configuration to the new card, neither successful.
I installed the SST Profibus configuration tool on the engineering pc and I tried searching for the PA devices on the network using the new SST card but only found 2 instruments out of 100 using both the ethernet option and RSLinx option. I have tried all baud rates but I knew beforehand 93.75 kbps was the correct option from the segment coupler manual.
I also tried connecting the SST Profibus configuration tool to the existing SST card to upload the existing i/o configuration without success. The manual says it is possible but I cannot get it to work. If I use the RSLinx option in the configuration tool I get an error 'opening rslinx connection to TCP-1 failed'. RSLinx Gateway is installed on the engineering pc. If I select the ethernet option in the configuration tool I get an error 'failed to read module id'.
How do I get the i/o configuration from the existing card or create a new i/o configuration by searching for new devices?
The card is on the plc rack. The plc is AB v30.011. RSLogix v30. RSLinx GAteway v3.9. All instruments are E&H PA using Pepperl Fuchs segment coupler. Connection from pc to plc is via ENET module on the plc rack.