ST v Ladder
norman oliver
Oct 2013
sutton coldfield
33
Hi, I have a program running which is, occasionally, giving me problems. Although I'm a ladder stalwart I've used ST and SFC in its construction due to the nature of the software ( Eurotherm PAC 9 with Eycon HMI & T2750 PLC ).
I have a 20 step SFC auto sequence and also a manual page/screen in which each individual device (e.g. door open/close, ram up/down, pump on/off) can be button operated for set-up or maintenance. Running the sequence requires these devices on the manual page to be off, i.e. Door_open:=0 for instance.
Could these manual instructions interfere with the running sequence, i.e. Door_open:=1 ?
If I had used ladder I would have a n/o contact in a auto/manual rung to isolate manual operation. How, using ST do I negate any instruction on the manual screen?
Your help would be greatly appreciated as I am quite new to using alternatives to ladder.
Hi Norman,
A poorly wrote program is a poorly wrote program no matter if its SFC or LAD so I would think the answer is YES, SFC is one I am waiting to learn once I retire :) but this maybe your time...
I would also think there has to be a way to write a NO in in SFC
Why you don't map io to seperate memory first?
You could then invert IO on ladder or ST beforehand.
Isn't here simpile NOT(myVariable ) command available?
I think if elseif is your tool here most likely without seeing the sequence.
If condition 1 and condition 2 then
This := true;
Elsif condition 1 and not condition 2 then
This := false;
Else
This := false;
Endif
Well, the simple answer is
Motor := Start & Interlock OR Motor & NOT Manual;
pretty simple however, ST is not really designed for bool (ladder is far simpler as you can see what is happening visually).
I hate IF then Statements they are long winded, can get confusing, use more code for example normally in compiled code the IF Else etc. use conditional jumps often to subroutines in some PLC's
This := true;
This := false;
Else
This := false;
Endif
Probably I would write with less lines
This := false;
This := true;
endif
Thank you all for responding - I will try your various suggestions. Meanwhile can you tell me the difference in using :=1 or :=TRUE and := 0 or := False and when is it appropriate to use either one or the other?
Hi All , I have used this to close the bottom door ST:"[OpenTD.OP]:= 0;" and :=1;" to open. They are two buttons on a "manual" screen and they work fine! The question is will ST:"[OpenTD.OP]:= 0;" interfere with a sequence that includes ST:"[OpenTD.OP]:= 1;" will the plc be confused?
Logical False / true is bit command and (used only for bits) and 0/1 is numerical which should used to word, ints and etc.
Both probably work for bit, but they are different datatypes and maybe can give compile error
I don't think that [tag_name]:=0; is valid syntax.
But if you are asking if you can have an assignment of a value to a tag in one statement and also have an assignment of a different value to that same tag in a later statement, then no, that will not "confuse" the PLC, because the PLC will do exactly what it is told: it will assign the first value to the tag when the first statement is evaluated, and that tag will maintain that first value until the second statement, after which that tag will have that second value.
The question is, is that what you want to happen, or are you confused about what the PLC will do with those two statements?
The point I am making is that PLC programming is primarily about time: so when each of two separate statements is evaluated is more important than what those two statements do.
Depends where in the scan order each falls.
There's about 100 ways to handle this aspect of the program, best practice in my estimation is to make sure subroutines writing to the same tag/output/whatever are not called at the same time, or the result will be defined by which one is processed last.
89
Hello, I am going over some old code from days gone by. I would like the expert to confirm my findings to see if I got it correct. 1. B64:22/3...
506
Hello, I´m having a problem trying to program in Ladder. An output should be trigged by two possible contacts. Take a look on the printscreen...
205
212
please help me . I have to make this ladder diagram and I can’t figure it out :(
440