"step 7 - wincc" can't see cause of failure
Avatar_41
Aug 2019
Istanbul
96
Hello there,
I need to find a fault in a system where the s7-300 and siemens hmi panel are interconnected.
Alarm number 327 is triggered via Wincc Flexible, address: "DB11.DBX41.6" appears in the "Trigger Tag" section.
When I enter "DB11", I see the screen shown in the picture named "DB11.png" and "DB11(2).png" below. (Data View / Declaration View)
When I type an address with the Go To option, an empty field appears.
After that, I don't know what to do. I will be glad if you help me. Thanks in advance.
They might be indirectly addressing the bits then. In which case, the go to location function will not find them.
Is there a specific FC or FB for alarm handling? I would start by looking there.
Example of indirect addressing:
Hello again. As you said Go to location didn't work. I found the address "M 940.6" by searching "alarm 327" from the symbols.
When I checked, it seems that the address "DB3.DBX74.3" should output. This fault seems to be related to the motor driver. "Siemens Simoreg DC Master" is a profibus etc. between driver and plc. no communication. In DataBlock, something like the following appears.
What should I do next?
Thank you for your answers.
By the looks of that ladder, DB3.DBX74.3 is an alarm from a drive, I assume that these drives are on a network connected to the PLC, the two contacts before it are so the alarm only occurs when in auto mode & data stream is normal, I suspect that the latter contact is something to do with the communications the bit is being set by what looks like a temperature alarm from that drive, somewhere I would assume there is a reset of that bit but it could be done by indirect addressing or as a word. if you go on-line on that rung, if the logic is true i.e. all three contacts are "ON" or at least the DBX74.3 is on then the alarm on the drive is still active, if not then there must be a way of resetting the alarms either by a button or a start system.
I suppose it is always possible the original programmer could of missed a reset of some alarms I have seen that before but you need to see if that alarm is still active by monitoring that rung, if so then check the drive it sounds like an over heat alarm.
There is no communication with the PLC over the network.
There are 7 different outputs named "simoreg temp". I guess "temp" doesn't mean "temperature".
But STAT221.STAT2xx seems to mean something.
I did not fully understand.
Please review the "fc1.pdf" file I shared below.
anyway thank you for your support.
View attachment FC1.pdf
You need to find out how DB3 gets written to...
as least bytes 73,74,75,76
Like you said, I dont see any communication being used.
I only see two binary outputs from the drive programmed
hello, thank you for your support. Coming this far is an achievement for me. Can you explain how you reached this conclusion? Shall I share DB3 with you?
At the end of the day today I did my first program edit in my customer's Simatic Manager project. It was the simplest of edits... add a bit with a...
2,327
Tomorrow morning I have to use a rented Siemens PC to troubleshoot a Siemens HMI, programmed with WinCC, communicating to a couple of ABB drives...
10,149
Hi folks, I'm new to Siemens and I have a couple questions: 1) In Step 7 -> Data Block : I try to read/write a bit in a word (like in RSlogix500...
5,392
i have wincc v7.0 sp3 andStep 7 v5.5 installed on windows 7 64bit how can i transfer tags between wincc and plcsim i did that in wincc flexible...
3,542
Hi all Hoping someone could point me to what I'm missing. I have a Step7 multiproject with a two projects in it (I called these B150 and WinCC)...
6,756