Strain gauge for silo level recommendations.
JaxGTO
Apr 2009
Kalieefornia
1,071
Customer does not want any silo penetrations. Hates level sensors on top of silos. No capacitance sensors either.
Would be great if it had Ethernet CIP connection (Logix 5000), but not necessary.
I though Keyance had them but I saw our rep today and he said they don't.
Thanks,
We have one on a powder silo, but I'd have to check what it is.
It reacts very, very slowly though. The level can take a few hours to peak after taking a delivery. It's fine for what we need, as it's just a rough guide as to when more needs ordering and it's not critical for the process.
I think you are after the kind of strain gauges that are attached to the supporting beams of the silo, i.e. it is not a load-cell per se.
Search for "silo strain gauge" and you will find plenty.
Since these strain gauges do not weigh exactly (in reality it measures compression or tensioning of the beam that it is attached to), you have to calibrate them after the installation with a full cycle empty-to-full.
There is also an issue with the supports for the silo. If there are several silos next to each other and the supports are shared, it may be difficult to find a beam that is only affected by the single silo which the strain gauge shall measure.
Sounds odd.
A strain gauge reacts practically instantaneously.
It can be necessary to add a filter since it may be too sensitive.
Maybe you actually have such a filter, and it is cranked up to maximum dampening ?
Hello, I'm currently working on a project where I need to read values off my 0-3kg Strain Gauge and display them on my HMI display. I've...
1,834
This is 99% a structural design flaw, but most people here have the capacity to manage this. First, some R&D background. I have a strain gauge...
1,488
I'm relatively new to working with plc's and I need some help. We need to run a fatigue test on a length of pipe and it will be controlled by...
2,049
CheezyMane13
C
I have 3 strain gauge transmitters I need to bench test the 4-20ma output. The transmitter 4-20 side is two wire with a shield. I do have a known...
5,080
After some advice on best makes for our application Pulling Wheels from Axles - Pull 50Tonnes Need to graph and record this, will be using a...
2,032