Strange plc problem
IdealDan
May 2017
MA
480
Hi Friends,
I have a strange situation at hand. I wrote a Logic for Tank Over fill (5 Tanks). When Level switch senses level, it triggers Alarm.
Same code duplicated for the 5 Tanks but I noticed that when PLC is Restarted, a False Alarm Triggers for Tank 5.
I have checked the code and I/O Assignments, everything is tight. replaced the Level switch on that Tank 5, checked wiring, used another input point on PLC (MELSEC iQ-FX5U)
Yet no joy.
Has any one here met this type of issue? or could it be PLC Battery as there is no battery in it and I could not see one locally.
I'll appreciate your input.
It would help you could post your code for the alarm.
One thing I have leaned id to put a 5 to 10 sec delay in the alarms this helps prevent false alarms.
Could be a dodgey sensor or transistor input circuit,
Maybe rewire that sensor to another input position. See if the problem follows or remains.
Also good practice to have a PLC Power up timer. Stop all logic from working until X amount of time after power up.
And also a debounce timer on the alarm as GaryS Suggested.
Troubleshooting is like invading a small to medium sized country - divide and conquer.
Write out everything involved in the water level high alarm, and pinpoint where it is.
Water -> level sensor -> cable - junction box - cable - terminals - plc card - backplane - adapter - Comms cable - Comms card - CPU - code - Comms card - cable - HMI - HMI program
There are also power supplies to various things.
Put a latch in the plc. Does it trigger? If so ignore the Comms to the HMI.
Disconnect the wire from the plc card and reboot. Does it trigger? If not, ignore your code and look at the electrics.
I always put a power on and stable logic into the program.
when the system power up, have a 1 second timer to ensure power is ok before continuing to the remainder of the program.
I have had to do this with several sensors.
24 seconds with Cognex camera interface board.
james
Honestly, I have done almost all of this things without result,
When I added a code Reset everything for the first 5secs of powering PLC, it resolves it but that same Tank 5 will no longer work
Could lack of battery cause this?
I just thought of this.
I copied programs from one system to the other (identical systems on the same machine) and had the same issue.
turns out I forgot to confirm the I/o addresses and failed to change an address.
also, I forgot to change a bit address from station 4 and left it on station 5.
that gave me fits for a good while. You might want to check that.
james
I don't work with the brand of Plc that you are using, but I think the logic would almost be the same over all plc's.
I always used a simple timer for all my alarms, this would be for debounce.
Example: the alarm condition has to be in the "Alarm Condition" at lease for a predetermined amount of time before action is taken.
2nd. If I am using any "latches" I always reset these latches on a power cycle because if the alarm condition is still present the latch will set again.
I agree with Ronnie Sullivan "Lets see the code" if this is a copy & paste type of duplication then one of the variables did not get updated.
I have Ge Fanuc 90-30 and Inet PLC , i want Connect by PME 6, i use cable which is working on another Ge Fanuc ,, The problem that after i...
17
11,849
So I had a strange problem today that defied what I've learned about data communication. basic setup is: Scanner -> PLC via RS-232 using only...
6,528
I was troubleshooting as to why a pump wouldnt start the other day and came across some strange goings on in RSLogix 5. If you watch the video...
5,910
I have an older PLC working as a Data acquisition and remote monitoring system on a piece of equipment. The PLC is approximately 1/4mile from an...
3,468
Hi All, This one is really weird. It may have been discussed but It's something new to me. Really knocked me for a loop. Anyway... I was...
3,704