Studio 5000 Communication issue
Elijah58
Nov 2012
Aiken, SC
60
Guys,
I am working on a RSlogix studio 5000 version 30 machine with a 1756-L83E ControlLogix 5580 Controller Rev. 30.011. What I have is an ethernet module slot 3 that seems to be correctly configured but my Zebra Printer Modules Are showing a comm fault, also there are several other modules on this network that are showing the same fault. I have tried about everything I can think of to find the problem with no luck at all. I can ping both printers and they are working correctly and configured properly. I just can't connect to them through Studio 5000. The error code is 16#0204 Connection Request Error: Connection request timed out. Any help would be greatly appreciated.
Thanks,
Eli
Does anything on that segment show up?
Di you try restarting your pc? might be a software issue.
What do the status lights show?
and is everything on one port or are you using both ports?
if using both ports are you sure the cabling on both is good?
has it ever worked?
and what is model # of printer?
has it ever worked?
Does anything on that segment show up? Yes
Di you try restarting your pc? might be a software issue. Yes
What do the status lights show? Flashing green
and is everything on one port or are you using both ports? One Port
has it ever worked? New Startup
and what is model # of printer? Zebra ZE500
Do you know the number of connections you are using?
you should be able to browse to the EN2TR page by entering it's address in a web browser
Could you link to the manual where you found info about the assembly insrance you are using? Is your plc code written already?
Zebra offered me to test a new beta ethernet/ip driver. I received the printer this week and the new firmware with EIP driver will be installed on september 6th, this way i will not use sockets but CIP communications.
I will let everyone here how this new driver work out.
I am hoping to use a MSG instruction to communicate between two CompactLogix controllers and was wondering if the Ethernet connection built into...
598
Hi Guys, First post here! I'll be working with PILZ Safety in a few weeks time, it will be communcating with Allen bradley, Studio 5000. I...
2,855
  • Poll
I created a program with 3 tags In1, In2 and Out (if In1 and In2 then out) and I downloaded it to my Emulogix 5868 (I'm using Studio 5000 logix...
4,779
Dear Network, I created a simple program with 3 tags In1, In2 and Out (if In1 and In2 then out) and I downloaded it to my Emulogix 5868 (I'm using...
4,038
Hi, I am trying to configure a CIP data table read MSG instruction to read a tag on a L85E controller and write to a L82E controller. The L85...
7,574