Studio 5000 - strange error , "conflict exists in project verification state"

I am trying to upload a test project to our 5069 controller we use for development and am getting an error I haven't seen before:


"Error: conflict exists in project verification state"



There are no specifics, it isn't a linked error that I can click on to see where the issue lay.


Google Searches are getting me nowhere.


Anyone run into this?


5069-L306ERS2 controller running v33
 
Have you done "verify the entire controller" ?
Do you see any Exclamation mark in Controller organizer? Like any hardware configuration that do not match?
Are you sure you mean upload?
We call it download to PLC, upload is getting program file from PLC to PC.
 
Last edited:
Have the BNOT_f in use?

https://compatibility.rockwellautomation.com/GeneratedReleaseNote.aspx?v1=58247&v2=58247&o=&pdf=0

Corrected anomalies for Studio 5000 Logix Designer, version 33.00.00

Conflict existed in project verification state
In a function block diagram routine, when working offline and adding a BNOT_f instead of a BNOT instruction, the Logix Designer application generated the error Conflict exists in project verification state. Internal error. Call Tech Support.
This anomaly first identified in version 32.00. (Lgx00227391, Lgx00227544)
 
Saw this error today while programming a L73S PLC. I fixed it by changing the controller type to a L72S then back to a L73S. Not sure how I caused it programming offline, but something must've reset by changing the controller type. Hope this helps.
 

Similar Topics

This forum post I found seemed to reference the same issue, and if posts were still allowed on that thread, I might make an account there to post...
Replies
7
Views
5,832
I am connecting to a remote device. When attempting to upload I receive an error that states: Error: Auto_Functions: The Import was aborted due...
Replies
3
Views
103
I recently did a program conversion from logix 500 to studio 5000 and when machine runs it depends on two ton instructions to keep the machine in...
Replies
17
Views
498
Hi Everyone. Not posted on here for a long time, but I am hoping someone can help me. I am doing a differential pressure calculation in a L27ERM...
Replies
16
Views
394
Back
Top Bottom