We have installed a sump pit at our facility that will be collecting water from floor drains and other sources. The pit has 2 pumps that will operate based on tank level. The water is pumped into a neutralization tank where it is neutralized before being sent to municipal drain. I was asked to install redundant level transmitters. I was wondering how any of you have done the programming for this type of application. My first thought was just to parallel the logic for each of the level sensors and if one fails the other will just keep things trucking along. Another thought was to use a copy or move instruction and use the data from one sensor and basically have the other in standby. Then if the first one fails I would start moving/copying data from the second into my level logic. The sensors can be programmed for failure modes of hold last state, empty, full, overfill(21mA), or overfill(21mA). I thought I would use one of the overfill failure modes to indicated a lost signal. The sensors we are using are ultrasonic transmitters with 4-20mA. I am using RSLogix 500 and our plc is a SLC 5/05. I have done many level applications but typically there is only 1 transmitter. Doing the redundancy thing is probably fairly typical in industrial applications but it's a new one for me. Any suggestions would be appreciated.