temperature controlled fan speed
jeff s
Aug 2007
washington
62
Hello, I have an application where I want to modulated fan speed with VFD to maintain a predetermined temp.how should I go about this?
How about a few more details
What temp, what volume of air, motor size, what will raise or lower temperatur 0f whatever you are trying to control.
If you cant supply this info please send batteries for my crystal ball.
Dan Bentler
Dan Bentler
Sorry guess i was vague this is for a 7.5 h.p. cooling tower fan the water is about 74 degrees and we like to cool to 70 degrees .On cool days i do not believe we need full fan speed to get sufficent cooling we currently have thermostat in return water tank and fans are on/off but they never turn off as some cooling is always required
Can't speak for other manufacturers, but I use Omron's (Yaskawa in the US) E7 inverter for exactly this application. Built-in PID, and the side effect will be a bit of energy saving too.
Have done this many times before.
You need a 4-20ma output to control the speed of the cooling tower fan via VFD.CONTROL VARIABLE.
In the cooling water recirculation tank is an RTD to provide the PROCESS VARIABLE.
Now you have a PID control loop.
Trying to make this a little clearer, you need two components. First, a water temperature transducer which mounts on the piping at the point you want to measure and control the temperature. This transducer preferably will have a 4-20ma output and will be powered by the current loop.
Second, you need a VFD with external PID capability. Many have this and many don't. You need to specify that without exception. Many drives with PID capability will also have a 24VDC power supply available to power the transducer loop. If not, you will also need a loop power supply.
Read up on the drive's PID system and build your temperature control system from that information. As mentioned above, this is not an uncommon mode of operation and you will be able to get support from your drive supplier or here on this forum.
Hello all, I'm a newbie so take it easy on me :-). I am currently experimenting with a solar water heating system. I would like to set up a PLC to...
31
11,571
I are working on a project using a plc to control a electric heater for boiling purposes (boiling a pot of water). i am new to plcs and have a...
3,152
I’m attempting to send a temperature from a SLC-5/02 to an EZiMarquee display. The vendor said to use a MSG instruction to send the data to the...
95
Hi!! I'm looking for Temperature rise calculation software from Rockwell, I just download "Product selection toolbox 2022" but this software is...
226
I have S7 1512C controler for controlling 48 PID temperature loop, the output is PWM. Please I need the best, most efficient way to write the...
619