Hi
I need to measure the temperature of fluid Viscor(similar properties to gasoline) but I'm not quite sure what type of sensor is suitable for my application​
based on their experience can you suggest me any brand of temperature sensor?​
with the following characterisitics
* Range Temperature to sense: 0 to 50 centigrade
* Output Sensor: 0-5V
Thanks in advance.
Hi
Thanks in advance.
Sure would be nice to have some details on process ie
is this in a five gallon bucket
in a pipe
pressurized vessel
What is purpose of sensing ie indication only or control
etc etc
Dan Bentler
Hi Dan,
Since it is only proof of mass flow that does not involve electrical tests, The purpose is to capture the temperature at which the test is performed and I need to mount the sensor in the tank viscor which is not pressurized.
In order to read the temperature I have a PCI DAQ (NI PCI-6034E) card with analog input channels (+-0 to 10V)
Thanks for you reply​
You need a 100 ohm RTD sensor in a stainless steel sheath
with lead wire to connect it to a transmitter
and a 24Vdc power supply (no photo) to power the transmitter.
Transmitters almost always output 4-20mA or 1-5Vdc
Most transmittes will output 0-20mA or 0-5 Vdc
Some transmitter might output 0-10Vdc but I wouldn't worry about it, just use the available 0-5dc signal and scale it appropriately.
Transmitter outputs must be ranged, so be sure to have your vendor range the transmitter for 0-50°C, so you don't have to get involved with the scaling software/hardware.
RTD's are custom made so buy a length long enough to reach wherever you want to measure the temperature in the tank.
Danw only forgot one thing. If it is like gasoline than you also need an EX isolation AI unit so it doesn't blow up.
Nonuke is absolutely correct. I didn't catch the hazardous condition. I should know better.
You'll need a transmitter which is rated for "intrinsic safety". Most are, but it needs the certification for such. It's a DIN rail mounted component.
The additional component needed in the circuit is known as a "barrier" or "IS safety barrier" which limits the amount of energy in the circuit in the hazardous area.
The barrier and the power supply are mounted in the "safe" area, some place outside the hazardous area around the tank where an arc, spark or ignition source could start fumes on fire.
There's an ATEX designation for IS but I plead ignorance, since I still use North American terminology.
It might be wise to find a vendor can source all the components, indicating that they have some expertise in the area.
Dawn you deserve 5 stars for the explanations.
A good supplier for this equipment is Turk.
I am looking for temperature/humidity sensor recommendations. Would like the sensor to display temp and humidity. Need to connect to a Contrologix...
238
Is there a way to configure a SystemTag in FactoryTalkView ME so I can use the integrated temp sensor for more than just the display intensity?
1,174
Good afternoon, I have an application where we induction harden different areas on our assembly part using coils that wrap around and heat up to...
3,749
Hello; I have arranged OPTRIS CSL-LT-SF laser temperature sensor to measure the temperature of corrugator web. I am confused about the...
2,872
Hi all, Trying to find a pressure sensor for an application where the process is running at -100°C (-148°F). Pressure is likely around 1 bar or...
2,949