Your transmitter is not powered.

Here's a generic diagram of what you need to do:

15mydt2.jpg


And an edited version of what you posted:

-
impe8x.jpg
 
My oversight error. I edited a graphic from the web to show the wiring.

The switch position should be the letter D.
 
2llirh5.jpg


If the statement above applies to the Siemens card being used, then a 2 wire becomes a 4 wire transmitter.

The industry definition of 2 wire vs 4 wire does not include the source of the DC power supply, but apparently it makes a difference for a Siemens analog input. It's their input card so you gotta play by their rules.
 
hi, i succeeded to get the value from the temperature transmitter :), now i need to connect another pt100 sensor to SM331 module, i don't have temperature transmitter for this sensor and i need to connect it directly to SM331 module, i have read on internet about wiring pt100 sensor with a 4-wire connection and i draw on this picture how i think it should be wired with a SM331 module.

An6vzl0.png



Is this wiring ok, or i need to wire it differently ?
Are this blocks for scaling ok, is this scaling gonna work this way?
 
Earlier you stated, "S7-300 PLC has a SM331 module (4-20 mA analog input)", so that card clearly can hancle a 4-20mA signal.

But a 4-20mA signal is a modulating current signal; an RTD is a resistor with positive temperature coefficient which needs an excitation current.

Why do you think that your particular board is compatible with an RTD? Does it have excitation current? Is there a wiring diagram showing an RTD connection to that specific board?
 

Similar Topics

I’ve been looking at buying a quantity of signal converters to take a type J or k thermocouple or RTD and convert it to a 4-20mA signal. In...
Replies
10
Views
3,007
Hello everyone, My name is Randy and I am an electrician/instrument tech. I have limited experience with PLC programming, and any experience I do...
Replies
13
Views
3,187
Good day folks. We've had to replace our boiler makeup water deaerator tank pressure transmitter quite often since commissioning the tank. The...
Replies
7
Views
4,024
I am looking for the symbols for a Thermocouple to mA adapter. I can find a P&ID symbol but not an electrical symbol for my wiring drawings. DO...
Replies
7
Views
3,786
Looking to add a some temperature transmitters (loop powered)for some control cabinets .. tracking and alarming. Looking for a cheap xmitter...
Replies
7
Views
4,301
Back
Top Bottom