Hi everybody
How can i connect a 3wire transmitter(4-20mA) to analog input card of siemens PLC S7-300/400.
One of my transmitter with two wire (4-20mA) failed.Right now i have similar type of tranmitter with three wire.What changes should i do to fix it with old card ?
In this new transmitter i see three terminals (+)power(7-30vdc) , (s)signal 2-20mA,(-)ground.
help
hi
thanks friend , but it seems very easy for you but for me , i m really confused.You might be talkinga bout some other PLC but in simens i see two terminals for one channel.:rolleyes:
Every PLC have 2 terminal each input + & -.
- can come from power supply or from the sensor.
If you have Transducer you might have 2 output wires.+&-.
They go to your card + to +,- to -,
3 wire analog input wiring
hi
It seems mickey is right to some extent.The power supply is part of input card if the card is configured for two wire.So +ve supply will be available at +ve of the analog channel and it will be connected to +ve of transmitter.
The signal wire will come back to -ve of the analog channel. and GND or -ve should be connected to -ve of power supply for card.
Hi everyone, I am part of a senior design group that is building a dynonameter to test shocks. We are ordering parts tomorrow morning and so I...
17
10,107
Aloha All; I have an app I need to develop to march data out of a Sensus water meter. The Sensus water meter uses ASCII characters and is...
28
19,829
Hi friends I got a PT100 Ohm RTD Automation Direct part number RTD0100-10-010-H .How in this case would I connect the RTD to a 3 wire device...
4,817
Hello Guys, I have tried the programming but can't twist my mind to make it work correctly. I'm using S71200 and TIA Portal. My system has...
208
Kindly, we connected electrical power, 3x380 vac, between a supply station and an electric cabinet, away 180 meters. The calculation software...
855