ti405 question

goxx

Member
Join Date
Jan 2005
Posts
84
i am using V1400 thru V1426, they all get a value during a fault, do some adding and give me a number. isn't there a way i can reset them all to zero using one box?

thanks, and happy st. paddy day!
 
If your CPU supports it you could use the FILL instruction. It takes a couple of loads to get all the information in that you need but it should work, assuming your CPU supports it.

Keith
 
yea, i can make that work, that's exactly what i was looking for. overlooked it in the manual, knew there had to be a way, tho. thanks a bunch, keith!
 