TIA Portal - configuring network

mccecim

Member
Join Date
Apr 2010
Location
Belem
Posts
24
Hi, I'm using TIA Portal v13. It's my first time that I have to insert a Remote I/O non-Siemens (Murr MVK-MPNIO DIO16 IRT) at the network. How can I do this?
All my inputs e and outputs are read and write through this remote I/O.
please...
=D
 
Hi, I'm using TIA Portal v13. It's my first time that I have to insert a Remote I/O non-Siemens (Murr MVK-MPNIO DIO16 IRT) at the network. How can I do this?
All my inputs e and outputs are read and write through this remote I/O.
please...
=D

Do you have the GSD/GSE of the Murr? If so, you have to import it via the GSD tool(HW Config menu bar) and then you can insert it into the network.
 
Hi, have you found and downloaded the gsd file for this. It should probably be available at Murr's website somewhere. Download it, start-up the tia and install it. Remember it's important not only to set the ip address but also the device name correct on your slave. Otherwise you will keep on having a hardware fault.
 
I downloaded the GSV and put the remote i/o at my network, but how can I put, for example, the first input (I0) of my remote I/O in my ladder program. the TIA don't identify the device by the name... how should I write the tag?
the normal tag for the inputs/outputs of the CPU is "%I0.0" for example...
 
I downloaded the GSV and put the remote i/o at my network, but how can I put, for example, the first input (I0) of my remote I/O in my ladder program. the TIA don't identify the device by the name... how should I write the tag?
the normal tag for the inputs/outputs of the CPU is "%I0.0" for example...
Well, when you pull the device into your hardware configuration, it will ask for the start address. You make that I0.0, if available. Once done and saved, you can right click on the IO module and edit symbols. Or you can go to the Symbols file and give I0.0 an unique Ragnar that you can use in your ladder logic. Remember to download to the controller before monitoring.
 

Similar Topics

I have been trying to connect my IM 151-8 PN/DP CPU over PROFINET in TIA Portal V11 and was able to Flash the LED and start the online...
Replies
12
Views
6,889
Hello, good morning, I have been having two problems with the Tia Portal software. The first is that I have installed it on my computer and...
Replies
5
Views
139
Hello all! So I have one project with a S7-1214 and a MTP1500 "Project1" and one project with another S7-1214 "Project2". Both of these PLC:s need...
Replies
6
Views
92
Hello, i am using profibus as communication between plc and fanuc arm. I can easily send inputs from plc to arm, but i can't monitor any outputs...
Replies
0
Views
42
Hello, I need to write the following program in Ladder language, but I could not integrate the Fibonacci sequence into the ladder. Can you help...
Replies
22
Views
461
Back
Top Bottom