Toshiba G7 vfd
reider
Sep 2012
meadow lake
20
So, here's the deal. I have a deck chain with a 5 HP motor attached to it. I have a foot pedal to stop/stop and an adjustable pot for the operator to use. So....... When the operator hits the pedal to start, the chain 'creeps' forward for about half an inch to 2 inches then starts 'creeping' backwards for a couple inches. I do not have a reverse on this chain setup at all. Is my vfd on its way out?
I'm not 100% sure I have this straight in my head. Could you explain the proper operation of the chain, and then what is actually happening?
I assume that this system has worked normally for some time and that this behavior had never occurred until recently?
Does it make any difference when the speed setting on the potentiometer is changed? Have you checked the voltage at your drive's speed reference input terminals while having the operator vary the position of the potentiometer?
I swapped out a powerflex 70 for a Toshiba G9 unit. The 70 is set up for 3 wire control coming out of the PLC (Omron) The user manual and terminal...
1,481
Has anyone had any success installing the Toshiba USB001Z USB to Serial Adapter to a Windows 10 PC? Is there a Win10 driver available? I use the...
2,540
We recently replaced a toshiba VF-AS1 inverter with a like new inverter. It has an ICC ehternet interphase card and communicates with a control...
1,175
Hello fellow members, Has anybody interfaced Toshiva VFD TOSVERT-300MVi with Rockwell's ControlLogix? Any examples? Regards, --Rahul.
3,569
Does anyone know where I can get a profibus interface card for a Toahiba G3 vfd? I thing the part number is IV3-PROFIBUS. Thanks
3,850