Totalise an instantaneous Flow rate
EICS
Dec 2008
Melbourne, Australia
323
i need to Totalise an instantaneous Flow rate in scada.
i will probably use the scada totalise function, just want to know if this code concept is correct for learning purposes
here is my concept , does this seem practical
Flowtag - Flow instrumentation will typically output a value around the 10.0kg per minute set-point under a closed loop system
Start Value - a register to hold captured instantaneous value
End Value - a register to hold captured instantaneous value
Avg Value - a register to hold averaged value over 1 Minute
Total Flow - a register to hold totalised value
the scada code below will be set-up as a continuous task which will run every 1 minute
  1. Avg Value = (Start Value + End Value) divide by 2
  2. Total Flow = Total Flow + Avg Value
  3. Start Value = Flowtag (capture value to register)
  4. pause 30 seconds then continue
  5. End Value = Flowtag (capture value to register)
  6. pause 30 seconds then continue
  7. loop to step 1
first scan will not be correct but otherwise ?
Your accuracy will depend on the how exact your 1 minute measurement is.
I belief you have an error. You are capturing a 30 second average, but counting it as 1 minutes worth. In step 2 you need to multiply Avg Value by 2.
  7. loop to step 1
What is your Flowtag?
If this is a Flow rate your code will not work.
If this is an accumulated what value does it roll over back to zero?
Typically if this was a flow rate ie 10kg/Min
Create an event ie Devx_Accumulate.
The trigger will be when Devx is running.
Set period for accuracy required ie 2 seconds
Action will be your Devx_accumulate_function()
Code:
Function
    Devx_Kgs = Devx_Kgs + (Flowtag / 30);
END//
can any one help with the math for converting an instantaneous value to a totalised value for Gas Consumption usage every hour. in the plant we...
3,248
Hi everyone this is my first post here. I have been reading a lot of the posts here regarding totalizing using pulses, however not exactly what I...
2,873
I’m working on two “Energy Consumption” projects for two different customers with two different PLC; AB1500 and AD260, the two most popular PLC in...
1,971
Hi guys. I'm trying to figure out how to calculate the instananeous power consumption here at the plant based on pulses counted off the meter...
3,711
Hi, I am using 3 motor pmps 7.5, 1.5 & 1.5 HP and respective FLA (full load amps)as per NEC code are 11,3 and 3 Amps. The customer would like...
2,903