Modbus AOI (and I believe the old application) supports only local EN2T module.
ControlNet bridging is not supported.
While Logix messaging supports bridging, this AOI uses sockets that works with Local Modules.
There is the answer OP has been looking for: they cannot use Modbus TCP protocol via an EN2T card on a remote rack.