Trending on RSLogix 5000 problems

beanpole_ecc

Member
Join Date
Mar 2011
Location
Ohio
Posts
48
This isn't a question but more like a FYI. I was using a bunch of trends (around 15) each fully loaded at 8 pens each. Over the course of a few weeks I edited the trends a lot to get them recording data in a way that shows the right details.

I noticed that after a couple months, the pens started to record the wrong data. For example, I had a tag array, Motor. Under this tag I had Command Frequency, Amps, Program Setpoint for the Command, etc. I wanted to trend the frequency which was 3 or 4 elements down the array. I noticed that instead of trending the commanded frequency of the array it would instead trend the setpoint frequency which was at the top of the array.

I tried deleting the trend and recreating it but I got the same behavior. After a couple weeks of troubleshooting the problem, I deleted the trend, saved the program, closed everything, rebooted the computer, then recreated the trends and everything is right with the world again.

I think the number of trends, maxing the pens for each trend at 8, and editing said trends repeatedly over the course of a couple months somehow corrupted something in RSLogix 5000 regarding the control of trend tags. It was only when I did the above steps that it finally cleared the issue and I was able to get good trend data. Simply closing the program and rebooting the pc did not solve the issue.

I knew it was a superficial issue because the program and system was acting correctly. The data being logged was incorrect. Hopefully, this saves the next person a lot of trouble.

Thanks
 

Similar Topics

I am familiar with trending data in rslogix, but can I export a trend table to excel manually or automatically? What are the steps if this can be...
Replies
2
Views
7,837
I have a application where i'm looking at using some data logging in a AB L43 processor with a PV+ 700. Instead of using force vs time i want to...
Replies
2
Views
3,128
I am studying how to trend in RSLogix 5000. The PLC is Controllogix 5000 (5571). As you can see in the picture I am attaching, I added 4 tags to...
Replies
2
Views
4,595
I've been online with a SLC503 for hours and created trends that I want to save and email later. Has anyone done this? Please help. Thanks a...
Replies
4
Views
4,500
Hello All, I am having a problem with some of my trends. I am using Historian tags in my trends. I have 2 clients that look at the exact same...
Replies
0
Views
860
Back
Top Bottom