Cf. here.
The Logix manual says the CTD instruction behaves like this:
But I think, and the flow charts on the subsequent pages imply, it might actually behave like this:
Could someone with actual knowledge and/or hardware please confirm which it is? My MicroLogix does the latter, AFAICT, but assuming the 500 and 5000 instructions are identical seems less than wise.
_
L75 controller V31 works as shown on second diagram - tested
Edit: Also tested L85E in V34 - second diagram is correct, DN bit goes OFF after ACC<PRE
My understanding of things is that the latter is correct (ie DN is true when ACC >= PRE). Give me a few minutes and I'll test with 5000 to verify.
EDIT: It does indeed in a 5380 running v32.
In fact, given that CTU and CTD adjust the DN bit regardless of the rung-in condition, it would be somewhat absurd to do it the other way -- otherwise any program that used both a CTU and CTD with the same counter tag/data would constantly toggle the DN bit when the ACC was equal to PRE.
Thanks both of you.
Yes, I though it seemed absurd as well, but with Rockwell I thought it was better to ask.
Those manuals are pretty good, a gold standard that makes all others seem like Pb, but there are still the odd typos.
On pg 30 (answers to quiz 6) I don't understand why the 3rd question is False and the 4th is True. According to the REGISTER LOGIC BITS CHART on...
1,533
Hi all I have a ControlLogix 1756-L71SP that i want to use for general PLC applications, not safety. I am running Studio5000 v33, i can't...
79
386
Hi, I have two quick questions: 1- Could I use 1756-IA16/A with TTL inputs? Sourcing (PNP)? Sinking (NPN)? Either one? 2- What does /A in the part...
182
Hi all, installed on chassis A17 an A/I from Allen-Bradley , problem is what ever I do , all channels are sticked on value 39.9 and cannot change...
155