US wire color 115VAC question
rQx
Oct 2010
Trelleborg
1,051
Hi!
I'm going to build a cabinet for US in IEC standard but we change the colors to the customer demand. It's supplied with 3x480VAC and I use a transformer to 115VAC. Normally I would use two colors for 115V, one for the phase and one for the neutral. But they have specified:
115V HOT = Black
115V NEUTRAL = White
115V CONTROL = Red
I'm not familiar with the term HOT. Normally I would use white and red here but what cables are HOT cables?
Thanks /Tim
Hot = L1 = Black
Neutral = Return = White
115V ac Single Phase.
Controls (Hot) = L1 = Red
Hot = L1 = Black
So the Control is also hot but is red? When is the hot used? This is only a control transformer. Or is the cable black from transformer to a relay contact and red after? Or is the HOT cable color only used if it is not switched? For example a 115 vac power supply to a PLC should be black and whte. But for the relay logic red white?
There is no official rule, but generally most people follow the color scheme laid out in NFPA79, which would call for the black to be line power, as in the 480V in your cae, red is the control voltage hot and white is the grounded neutral.
Ok, if I had 115 directly from the line to my cabinet it would be black. But since this is from transformer it will be red. Think I get it now.
So they just included that 115V hot is black to confuse me (y)
They may mean if anything on the machine is 120VAC they should be black wires - solenoids, mixer pumps, vibrators, etc.
Red wire would be 120VAC for pushbuttons, relays, proxy's switches, etc.
In our practices, Typically the incoming voltage from the customer prior to any transforming is ran with a Black conductor. If we need to implement a transformer to step it down to a lower voltage, then that conductor regardless of function should be Red.
In a single phase setup the grounded conductor is always White while in 3 phase they are typically all the same color.
Thanks for all the help I see how this should be done now.
On a side note:
We had two diffrent customers wanting diffrent color on the 480VAC incoming power.
One said all should be black and one said, brown, orange, yellow.
What is most common? All black or diffrent colors?
Brown Orange Yellow is a european standard for 3phase AC. If the machine is staying in North America, all Black is typical.
On a side note:
Typically large conductors are "phase taped" (marked with B/O/Y tape) at termination points. Smaller conductors use B/O/Y insulation.
Brown, Black, white is the european standard. I got this from our american customer saying that this is the US standard??
I get confused when timryder says that 3x480V it is all black in US and that BOY is european standard. Then Automax says BOY is the US standard for 3x480V
Bottom line, BOY is US standard. Larger conductors can be taped?
Dumb question, Hooking up two wire reed switches out in the field. They are wired into sinking input cards. Once the wires leave the panel, do...
1,504
We are creating a CE compliant version of one of our products, for sale in Ireland and the UK. We would like to use Brown for VDC+ and Blue for...
3,962
Good Morning , I'm building a control panel with PowerFlex 525 drives. I have black wire for the 480 vac , red for 110 vac , blue for 24 vdc...
2,905
What is the US standard color coding of the high leg and other phases in a delta circuit? TIA This is what I have:
3,519
Do you guys know what the wire color should be for a DC External source when going from one control panel to another? I read yellow or orange but...
2,888