Vector control VFD?
LowRange
Jun 2016
Omaha
52
I would like to monitor the torque current parameter on a Powerflex 525 drive with embedded ethernet but my understanding is that the drive must be used on vector control to separate the torque current from the output current.
I'd like to know what I am getting myself into. What exactly is 'sensorless vector control' and how does it differ from V/Hz? My intended application is to monitor the torque current parameter to detect a jam condition on a rotary bottle filling machine. The machine has crashed into itself on a number of occasions bending shafts ect.
It is my understanding that you won't be able to do what you want to do. AB's sensorless vector control strategy doesn't allow for separation of flux and torque producing current. Sensorless vector control attempts to determine rotor speed based on the measured current and voltage at the motor terminals and adjusts the output voltage vector to influence the rotor speed. Think of it kind of like intelligent slip compensation.
Flux vector control would allow for determination and control of torque producing current. But I think you would need an encoder for that with the PF525.
In any case, are you convinced that any drive would be able to respond quickly enough to reduce torque in a crash case before mechanical damage is done? "Electronic Shear Pin" is a touchy little gig in many mechanical drivetrains.
Keith
To understand SVC, you first have to understand "regular" output from a VFD, called "Scalar" or "V/Hz" output. At this basic level, the VFD puts out a voltage and frequency commensurate with what the motor is designed for, which determines the torque it produces. So a 460V 60Hz designed motor requires 7.67V/Hz (460 divided by 60) to produce rated torque, ergo a scalar VFD spits out 7.67V/Hz. So at 30Hz the voltage is 230V, at 10Hz the voltage is 76.7 etc. etc. This output from the VFD has to provide the excitation (flux) current to the motor as well as the "torque producing" current all at once. So when something in the load changes, the VFD can only respond by giving more current to produce more torque, but at the same time more flux current, even though the currents are flowing at different portions of the size wave; the flux current goes first, followed by the torque current. Because they are increasing together, the excess flux saturates the windings magnetically. So when the load changes (a "step change" in load) with scalar control, the motor slows, the slip increases, that causes the motor to draw more current, which increases torque (AND flux) and eventually the load speeds up again. How long that all takes is a function of the size of the step change in load and the torque capability of the motor. It might take seconds, it might take minutes, it might cause the motor to overload if it takes too long because that excess flux is turning into waste heat.
With Vector Control, the reaction that the motor has to the change in load is monitored by the VFD and the output wave form is altered sub-cycle to "tweak" that V/Hz pattern such that the torque producing current is increased WITHOUT needlessly increasing the flux producing current, each of them measured as vectors of the total current. So more of the energy going to the motor is doing useful work and that allows the motor to respond to that change in load more rapidly. To accomplish vector control, something must tell the mP in the VFD exactly where the rotor is at any given moment so that it can crunch the numbers to know precisely how much torque to apply to affect the desired change. That rotor position measurement was originally accomplished with shaft encoders that fed that data back into a motion control positioning loop in the drive. By making the motor react more precisely and quickly, the "drift" of error in speed (or torque) is corrected much faster; measurable in radians rather than seconds. That allows for more precise control of whatever you need control of.
Vector control has several variants and sub-variants. SVC, so called "sensorless" vector control, is a later development that eliminated the need for an external shaft encoder by looking at subtle changes in the current waveform and comparing that to a mathematical "model" of the motor that is created in the VFD's memory (via tuning to the motor). So SVC is not looking at rotor position with EXTERNAL sensors (shaft encoders), but neither is it really "sensorless" because there are still sensors, they are just current sensors INSIDE of the VFD itself. In addition, the rotor position is not absolute, it is only relational; compared to a previous moment in time and the model. It's far more accurate than basic V/Hz control, but not exactly high precision. So it has limitations, especially at very very low speeds where the signals become too weak to detect. Because of this relational positioning, it's not really possible to totally separate the flux producing current from the torque producing current. It's better at it, and for a vast many applications it's good enough.
If you need more precision, you go with Flux Vector Control (FVC) or another sub-set called Field Oriented Control (FOC). Then even within FVC, there are two sub variants; Velocity Vector Control and Torque Vector Control, based on what you want to accomplish; speed or torque control. Basically, each requires a separate regulator loop within the mP (or DSP). Simple low-cost drives, like the PF525 or PF40, are only capable of Velocity Vector Control when using the encoder feedback, but do not have the mP power to add the Torque Regulator Loop algorithm; that requires a more powerful (and expensive) mP (and/or dual processors), which is what you get with a more advanced drive such as the PowerFlex 70/700/750 series.
So how does that relate? If what you are really after is the equivalent of an "Electronic Shear Pin" protection functionality, you may find that the PF525 functions that provide that (A455-458) are good enough, it will be as good or better than any COTS Electronic Shear Pin relay you can buy. But that's not the same as "separating flux current and torque current", which the PF525 is not totally capable of like the PF755. However, you don't really need that capability just to enable an Electronic Shear Pin, that's more applicable to torque control applications such as winders.
HI,
DAMN, you guys are smart! I learn a lot just by hanging out on this site. This is useful info that helps me.
Rock On
BD
If only the drive manufacturers would bring out the power factor as a parameter, we could easily find a torque point :) After all, it's the root of the vector calculation.
The whole 'sensorless vector' or 'open-loop vector' function has been implemented so differently, and with so much of a variation of accuracy in different manufacturers and different models, that it's not a sure-thing.
That said, it's certainly worth a shot to try. Particularly if you normally run at a fairly consistent speed and with fairly similar motor temperatures. (Don't forget that since the winding resistance varies greatly with motor temperature, so does the power factor and thus any torque calculation.)
:geek::geek::geek::geek::geek:
It's for posts like this that we need a "Thank You" button! Incredibly informative post! Thank you Jraef for taking the time to share your knowledge with us!
Can someone recommend a good site to explain Vector Control on a VFD please. I google'd it but this PC I'm using takes about 10 minutes to open...
2,249
Good Afternoon , I am getting ready to refurbish 2 machines . It will have 3 SEW gearmotors on each machine. I would like to keep the...
3,730
Hey Guys, I am having a tough time in understanding the philosophy of vector control of induction motor.I have referred to atleast 10 - 15...
6,235
Hello experts i am new in automation field i need spare part list of simovert vector control drive.
1,774
Does anyone has an idea in what range the speed of a sensorless vector control driven motor will deviate from the real measured speed?
2,388