Wago 750-862 Auto-run problem

sumit.sharma

Member
Join Date
Feb 2024
Location
Italy
Posts
4
Hello,
I m having a problem with wago 750-862 plc.
The plc won't start automatically in run mode after a power reboot.
I've also tried the boot application but same thing continue to happen, the plc is not starting automatically in Run mode. everytime after a reboot I have to go online with plc and put it in Run mode.

Also they have the latest firmware installed.
 
Hi Darry, thanks for the quick reply.
I havent worked much with that plc model and it is already installed to the client.
I dont remember any stop/run witch on it.
If I go online with codesys 2.3, I m able to put it in Run mode from codesys, but when they power down the entire cabinet of the machine they also cut the power for wago, and when they give back the power the plc stay in stop mode until I go again online with plc and put it in run mode.
 
Yes, there is a cover on the face you flip up. The switch is there. Sounds like it's in the center position for stop. Needs to be in the top position for run. Whichever position the switch is in, you are able to change the mode when connected with your software. (which you are doing) But if the switch is in the stop position, the unit won't do anything at powerup. Have someone make sure the switch is in the top position.
 

Similar Topics

Does anyone know how to set the time and date programmatically in the wago 750-862? Or direct me to the library that I need & link? I am using...
Replies
2
Views
1,619
I know someone out there has code to programmatically set the plc time and date. It would save me a ton of time if anyone could share this w/ me...
Replies
4
Views
2,692
Is it possible to increase the area that retentive %MW registers reside. Aka, is it possible to address them at %MW4096 and above w/ a software...
Replies
10
Views
2,830
Hello, I am in possession of a WAGO PFC 200 750-8216 which I was successfully able to set up as a Modbus RTU Master to a slave device using...
Replies
0
Views
84
I have a project to setup base programs across multiple PLC platforms that can be used for Modbus communications to various sensors that have...
Replies
0
Views
122
Back
Top Bottom