Weird Fault on MicroLogix 1400
Tim Ganz
Dec 2010
Dallas, Texas
704
I have a fault on a micrologix 1400 that says" The controller cannot communicate with an expansion i/o module. The exact module cannot be determined"
If it doesn't know which module how does it know it can't communicate?
Anyone seen this before?
It probably knows a module is there but cannot get it's details. or it is expecting a module as per the settings for the I/O but as it cannot talk to it, it does not know if the module is faulty or wrong type. there could be a number of possibilities like bus connection poor, module faulty or backplane faulty. (depends on the PLC backplane can effectively be a rack or interconnecting plugs & sockets if the modules are used where they are daisy chained rather than onto a rack.
I have seen a fault similar with a Micro 1400 whereby the fault message indicated that there was a fault with an expansion I/O module.
When we replaced the expansion I/O module, the fault remained, so we had to replace the Micro 1400 controller.
Best to have spare parts available for both the controller and the expansion I/O
I don't have a whole lot of experience with RSLinx Enterprise or I guess it's also called FactoryTalk Linx. We have a Rockwell FTView SE based...
48
I have created a project in TIA Portal v16 Upd6 with S7-1200 (6ES7214-1AG40-0XB0) and WinCC Unified (PC station). The communication between the...
191
I currently have a weird issue involving Ethernet IP communication between a ABB CI873 (EthernetIP Module) and a 1756-L83ES. The Layout is as...
807
Good morning. I'm doing a rehab and I need to recycle some part of the old code that won't change and that I need. This is a calculation that...
22
1,476
I'm trying to figure out a weird behavior I'm seeing in my CCW program. It's for controlling a gas polarizer (for medical imaging). I'm using an...
476