Weird thermocouple reading behavior
hagaib
Feb 2014
israel
Hey all,
i have a friend with an application where he has a "black box" which is comprised of a heater and a thermocouple (4 wires coming out in total).
he's using a B&R digital output module to turn the heater on (i.e. give it 24V) and a thermocouple module to read the temperature from the TC sensor.
with one of these "black boxes" he has encountered a strange phenomenon - once the reading from the thermocouple reaches a certain temperature (and the digital output giving power to the heater from that same "black box" is still on), instead of climbing, the temperature reading begins to drop. Once the output from that same "black box" is turned off - the temperature reading jumps to what it was supposed to show if it hadn't dropped.
other than a defective sensor ("black box" was changed and the phenomenon stayed), do you have any other explanation for why this would happen?
Thanks.
Back circuit. The 24DC powering the output is also powering the analog input electronics.
Use an isolated tip thermocouple. Isolate the heater. Use a dedicated supply for the output.
Solution!
saw it today first hand and solved it.
quite weird - it's a model built of an IR heater and a thermocouple.
one was working fine and the other showed the phenomenon i described before.
turns out that B&R help recommend connecting the thermocouple's COMMON to the PLC's COMMON, once i did that, issue was solved!
I have created a project in TIA Portal v16 Upd6 with S7-1200 (6ES7214-1AG40-0XB0) and WinCC Unified (PC station). The communication between the...
147
I currently have a weird issue involving Ethernet IP communication between a ABB CI873 (EthernetIP Module) and a 1756-L83ES. The Layout is as...
761
Good morning. I'm doing a rehab and I need to recycle some part of the old code that won't change and that I need. This is a calculation that...
22
1,372
I'm trying to figure out a weird behavior I'm seeing in my CCW program. It's for controlling a gas polarizer (for medical imaging). I'm using an...
465
I'm trying to figure out some weird behavior I'm seeing in one of my programs. This should be fairly straightforward - except that it's not...
954