Which PLC for just 1AI & 1AO signal?
ckchew666
Aug 2003
Malaysia
591
We have a very small project using PLC to control the pump to maintain a constant pressure for a water jet in a system.
There is an analog input from the pressure sensor (4-20mA) and output (4-20mA) is to a drive (to control the pump).
When the input from the pressure sensor is low, the pump must run faster to maintain the pressure. The pressure is fix and not adjustable.
Customer specified for either OMRON, Yokogawa or AB. Which ever cheapest. But I guess OMRON is the cheapest....but I'm not sure which model is suitable...can anyone please suggest.
No network or scara/touch screen.
Why do you need a PLC at all for this? Most modern drives provide at least PI control for this type of application so you should be able to do everything you require in the drive.
Why not a single loop controller? Small, inexpensive, and you have a display of all your parameters. You can also easily place the loop in manual, and do trouble shooting, maintenance etc...
You could use a ML1200 with an analog module, but the single loop is cheaper, and in my opinion a better choice for the application.
Agreed.
If you have to use a PLC, Omron CPM1A is probably the cheapest but I would certainly tackle the job with a drive only.
Please take a look at the attached example "Complex application 2".
This is the simplest way
Thanks for all the replies :)
Where's the attached sample?
Yes, customer insists on the PLC to control the simple (1AI, 1AO) pump machine.
Looking the price for CPM1A + expansion module, we are thinking to checkout the PICO controller, I think it's cheaper than CPM1A. It has 4AI & 1AO, we never use/see any PICO before....will get the price from Rockwell on Monday :)
The CPM1A + 1 MAD01 cost around RM1800 = USD450.
Have a look at the Mitsubishi Alpha2. It is a smart relay with analogues, RTD and thermocouple inputs and you can program the screen display.
Also remember that the Pico is just a Moeller Easy in disguise, so be sure to compare pricing from both... :nodi:
-Eric
Bob: Thx, i'll check it out also.
Eric: Wow! I do not know that until u tell me PICO is from Moeller :) Great info, I'll check out the price with them as well. Not sure if you know this - jst to share, the safety switches/push buttons selling by Rockwell, it's actually from Bartec :)
Yes, the Pico is the Moeller Easy. One thing to know is that you cannot use the AB software on the Moeller brand device and you cannot use the Moeller software on the AB brand.
In order to get an analog output, you need to have a Moeller Easy 820 or 822. I don't know what the equivalent Pico numbers are.
It's okie, i'll chk with moeller. Thx for ur info.
For a small and reliable PLC, use the Allen Bradley MicroLoxic 1000 Analog model.
Part Number: 1761-L20BWA-5A or 1761-L20AWA-5A
Cost is cheaper than Omron or Mitsubishi. Has Two analog input, voltage or currend selectable. One analog output, voltage or current.
Thanks,
Swimmy67
Hi all, looking to model old RR relays in PLC. Does anyone have any SPECIFIC examples on how to model a relay such as a polar relay, slow pickup...
82
HelloI need software to download the program from PLC EH-A28DRP from an old machine whose manufacturer does not exist. It may be Ladder Editor for...
75
HI everyone, i am new to Siemens plc programming and i am in need of some help. yesterday we had an S7-1200 CPU 1214C fail to turn on an output to...
292
Hello, I have a Mitsubishi FX3G 14M PLC and a E615 HMI from Mitsubishi/Beijer. I'm using GXWorks 2 to do the programming and I have no problem...
149
Hi, I'm trying to import a Rockwell/AB EDS to Beckhoff but I'm not sure how to import/install the EDS. It is a PowerFlex 525 EDS. Is there a way...
109