Why does this work?
f16bmathis
Sep 2013
Wisconsin
131
Prgram was not working, a 5/05 that should turn on a pump through a latching output when level gets to 60% or more (GEQ). Used a SCP for the sensor, and another used for output to the motor. The unlatch would happen at 20% or less (LEQ).
Problem was the motor would latch on at 20% and turn back off at 20%. I found the SCP for the motor was set as 0.0 for scaled minimum, and 100 for scaled maximum.
When I changed it to the same values the 4-20ma sensor was set at, the program started working normally.
So my question is... Why did changing the SCP for the motor, allow the program to turn on at 60% and not 20?
As far as I can tell, the SCP should have no effect on the motor turning on or off, but it does, so why?
Thanks!
1. Can you post the program - you'll have to zip it (forum rules).
2. I don't like the idea you have "latching outputs", there are safety issues involved.
Ooops, just realised I don't have RSLogix5, but there's loads of people here who do.....
If you have RSLogix500 you should be able to help. (SLC5/05) A PLC5 does not have a "SCP" instruction.
To the OP,
If and when you post your program, post the version that was giving you trouble. Also the corrected one.
And point us to the rungs in question.
Hi I have a ifix 5.5 application where the operator opens a valve by clicking on a screen object. I can trace from object to data base that it is...
41
Hi, i am using DVP-14SS2 PLC, after program written to plc, when power is reset, plc doesn't run. always need to connect to pc for the run mode.
34
I am trying to connect with a Schneider plc which has a firmware version only available in Somachine v4.2. In Machine expert After taking upload...
122
They are installed in a control panel that was made in France and are intended for the termination of analog inputs. Each of the red capped...
432