WINCC RT no data from plc

zxced

Member
Join Date
Mar 2021
Location
Angeles
Posts
13
Hi,

So we have 3 pc with wincc rt installed. I have the program in my laptop and downloaded to file system the scada file, transferred it to the 3 pc and opened it using wincc rt. I configured the device, was able to ping the plc but there's no data coming from the PLC. It's showing greyed out background from transmitter(4-20mA) and no data.

I am not sure if Set PG/PC interface is needed If so, is there a way that I can install Set PG/PC interface without installing TIA Portal since the 3 PC's are going to be put on site for the client? Do I need license for this?

Thanks.
 
Is this TIA WinCC Advanced RT ?
Yes, it is necessary to set S7ONLINE. You do this in PG/PC Interface or in Communication Settings. Both of these are usually installed together with TIA WinCC Advanced RT.
You shall also program a message view for system messages. This will pop up a message with some information with why the HMI does not go online.
 
Hi,

Thanks for response. This is wincc rt professional.

Unfortunately Im still having trouble. I configured the Set PG/PC to S7 online>tcp.auto<active>

Then at the TIA, the hmi communication is configured as well to their responding IP addresses.

Then I downloaded to file system , transferred it to the PC station, still no luck.
 
I dont have experience with WinCC RT Professional. But I think Advanced and Professional are similar for this topic.

I have better luck with setting S7ONLINE to TCP, without the ".AUTO".
Can you post a screenshot of the connection setup in TIA ?
Also, like I said you need a message view for system messages. Chances are that there is a system message that says exactly why the HMI does not go online.
 
Hi,

Sorry but I cant attached screenshot here. Im using my phone for the forum. And i tried attaching pictures but it's just saying to put the link or url of the image .

I tried using without the "auto".

I was able to gather data using my laptop but when I tried it on the client pc, still no signal.

I am not sure where to check the messagw view for the system message.

Thank
 
I noticed that in the hmi connection, my laptop where the project file is open, hmi connection used the tcp ethernet adapter of the laptop and it's different with the one in the Client PC. Would that make a different?
 

Similar Topics

Long story short, I am trying to map a DWord-type PLC tag as a Real-type HMI tag. I have a structure that stores arbitrary data, so depending on...
Replies
4
Views
3,585
Hi all i am using STEP7 V5.5 SP2 HF4 & WINCC V7.0 SP3 on a 64bit PC with Win7 Ultimate I have : 1. One UDT block in STEP7 project (Figure UDT) 2...
Replies
7
Views
3,664
Having a problem with WinCC. If I go into the receipe screen and then exit said screen without doing anything all my tags in the PLC have been set...
Replies
3
Views
2,777
I have only a small amount of experience handling PLCs, one thing I wish to do is print out data from the PLC. I am using S7 and soon use WinCC to...
Replies
0
Views
6,457
Hello. I have a db which is 1000 INT, and this db is represented in WinCC as a raw data type set of 5x 400 Bytes. This set is read with a script...
Replies
1
Views
76
Back
Top Bottom