WonderWare 2012 Alarm Pop-Up
Managh
Apr 2017
West Midlands
Hi, fairly new to using WonderWare.
I've been asked to create a new project which monitors temperature. I want to create some alarms that pop-up when the temperature reaches a certain value, just displaying a warning message to an operator. I've created the pop-up screen but not sure how to activate it when the temperature reaches a certain level.
Can anyone help with this?
You could use a Condition Script that is triggered when Temp_Tag >= Alarm_Temp_Value
Use the "Show" or "ShowAt" function to open the pop-up window.
This can get really annoying when you're trying to use an HMI and a window keeps popping up, which can happen if your reading is fluctuating around your alarm point.
I would set up an alarm on the tag (see tag database, alarm tab) and use the .dotfields for the alarm to cause the popup to occur. Only do the popup if the alarm is unacked.
See the help files for more explanation of dotfields
If you want to avoid nuisance alarm window pop-ups due to a fluctuating signal, using dotfields would not be the appropriate solution. What you'd need to do is to create and reference a discrete alarm in the PLC that employs a timer (or timers) to prevent oscillation.
You can employ deadbands with tag based alarms, but you can't employ time delay.
There are many ways to do this....
Average the signal
Create timers
Use the UnAck dot field
For environmental type alarms, we'll usually use a reset timer. The initial alarm pops up the window, and the operator can acknowledge/close the popup. This action starts a timer in the PLC that once timed out, will relaunch the popup window if the alarm is still active.
Average the signal
Create timers
That's not necessary in InTouch with a condition script. You may show the window immediately with Condition Type: "On True", and set a time delay for showing the window again with Condition Type: "While True".
I'm working from some spec documents that declare I must allow the operator to set an alarm delay for any alarm signal. I would like to use WW's...
3,807
I completely uninstalled Wonderware 2020 and all the related components, rebooted, and then tried to install InTouch 2012, but it won't proceed...
2,049
We have a 2012 Wonderware system running on an older driver setup. ( 2 Servers with about 15 PLCs connected) In each Server, we have an...
928
Can any one shar a compatability matrix for WW 2012 shoing newer OS what is the highest version of MS Server that this support or are we better...
951
Greetings I am having a problem with a 10 character tagname limit in Wonderware 2012 R2. I imported a graphic. The tags are set as placeholders...
6,801