georgevjoel Member G Join Date Jan 2024 Location kerala Posts 1 Jan 17, 2024 #1 can i send and recieve data using my yokogawa UT35A controller with my siemens s7 1200 plc using profinet communication without using gsd file
can i send and recieve data using my yokogawa UT35A controller with my siemens s7 1200 plc using profinet communication without using gsd file
Puddle Member P Join Date Mar 2022 Location UK - The Norf Posts 331 Jan 17, 2024 #2 You need a GSD file for anything that doesn't appear in the hardware catalogue on TIA portal. Does it have Profinet though? It says Ethernet and Profibus but doesn't actually specify that Profinet is an option. RS-485, Ethernet, PROFIBUS-DP, CC-Link, DeviceNet Click to expand... On page 1-8 of the user manual it says that the Ethernet port can be used for Modbus TCP which you won't need any additional hardware for. Profibus and Modbus RTU would both need communication modules.
You need a GSD file for anything that doesn't appear in the hardware catalogue on TIA portal. Does it have Profinet though? It says Ethernet and Profibus but doesn't actually specify that Profinet is an option. RS-485, Ethernet, PROFIBUS-DP, CC-Link, DeviceNet Click to expand... On page 1-8 of the user manual it says that the Ethernet port can be used for Modbus TCP which you won't need any additional hardware for. Profibus and Modbus RTU would both need communication modules.