You never know--how do it do dat???
This is the ladder logic that will illistrate my crazy experience, last week.
[attachment]
OK, The circuit/logic was designed to tell the operator which safety gate is/was opened first. An alarm indication to a screen. If 304 SR contacts open, both inputs I:0/7 and 8 are turned off simutaneously, and N11:0/4 should latch. The EQU statement at the first of the rung prevents any other N11:0 bits latching in after the first one does.
If 305 SR opens, only I:0/8 is off and N11:0/5 latches, right???
That's the way things should work, here. If they both go away, I know the first in line did it, if only the second goes away, I know the second one did it. (by the way, the two circuits are combined so I could use one pair of CR's for two SR's instead of two pairs of CR's--both CR's are monitored by both SR's.)
But it didn't work that way. When I open 304 SR, N11:0/5 latches--then because of the EQU, n11:0/4 can't come in. If I remove the equ's, they both come in--/04 and /05. There are 4 pairs of gates wired/programmed this way but I see the problem only here on inputs /07 and /08.
The only explanation, I think, is that the /07 input "lingers" a little while longer than the /08 input when power is simutaneousl removed. A histogram displayed them as simultaneous, but the ladder will scan several times during the shortest histogram period. Anybody got any other ideas??
The controller is an AB ML 1500 DC input type. And there are 5 of these applications installed. I have noticed this "inaccuracy" on one or two of the others, but only got a chance to chase it down last week. The only problem was hat the wrong guard was indicated as opened.
Anyhow, the result of all these hardwired relays is an MCR. So I wait till i see that gone, then wait .25 sec and check the gate inputs for the indication and that solved the problem.
But this thing proved to me that things are not always as they seem.
Histogram doesn't have scan resolution and it's not good for fast changes.
input signals are usually not filtered in software.
Inputs are connected through simple RC filter and tolerances for capacitors
are usually higher than for resistors. Then you also get the different curve
for every optocoupler's LED...
your logic is expecting that all tolerances of the input filters are less than one scan. while this might usually be the case, it is not guaranteed.
Why don't you simply add small timer (50-100ms) to delay I:0.0/07 in second rung and leave NC of the i:0.0/08 as it is?
Using an L81 - I have the arrangement below that will try the Ethernet Radio first and if that fails use the Cellular Radio. The Failover works...
3,405
We have just recently had an "outside" organisation upgrade our AB SLC PLC with a Controllogix. In doing so they have changed all of the messages...
1,810
I got involved with Modicon when we were asked to make motion controllers for the old 984 PLCs. Back then the programming was done using Modsoft...
2,515
Insurance companies share information to other companies. Why don't us automation part buyers share this pricing info. Because we getting the best...
27
6,381
Rookie question I want to run Ethernet from PLC cabinet to HMI cabinet some 27 feet away. On this project we are using cabling to connect remote...
7,141