Zelio relay damage

Ice-Tea

Member
Join Date
Nov 2012
Location
Belgium
Posts
4
Hey,

Have 2 ZELIO PLC modules, mainly to switch the lights inhouse. Unfortunately, the relays have a tendency to "stick", the last one with a grand total of 29W of CFL on a 5A relay. Aside from venting my displeasure, I'd like to know if anyone here has refurbished relays for Zelios and would like to share their experience?

Ice-Tea
 
No specific experience with the ZELIO PLC, but if it's built like most others, the relays are probably replaceable, possibly using a soldering iron. Some relay modules allow you to replace damaged relays through the use of a socket arrangement.

CFL lamps, even they "only" draw low wattage, have very high inrush values. That's why your relay contacts are welding. I strongly suggest using an interposing relay that has the proper rating to switch a load with high inrush.

-rpoet
 
Well, I was afraid you might say something like that. I specifically installed the Zelio because price per relay was pretty uch the same as for discrete "dumb" modules. Didn't count on having to double them all :D

Well, I'll pop it open then. Maybe I can replace the relays with higher rated ones. Some version even have specific inrush current versions... If I find the time I'll post some pics/findings.
 
Maybe I can replace the relays with higher rated ones. Some version even have specific inrush current versions... If I find the time I'll post some pics/findings.

I doubt you'll be able to replace the relays with higher-rated versions; the PC board space on those modules (or any PLC module) is pretty tight.

Chalk this up to a learning experience; the best solution is to use a DC transistor output card, and use it to control hockey-puck style solid state relays. Nothing mechanical to wear out, and the solid state relays are easier to swap if you ever have an overload that damages them. If you oversize them slightly, and protect them with appropriate fuses, you should never have a problem.

Solid-state relays are easy to find on the surplus market, and can be pretty cheap.

http://www.surplussales.com/Relays/RESSPlug-1.html



-rpoet
 
I doubt you'll be able to replace the relays with higher-rated versions; the PC board space on those modules (or any PLC module) is pretty tight.
-rpoet

True, off course, but in the same series/FF of relays there are part numbers that have better inrush current ratings (but identical steady state ratings). Has to do with plating of the contacts.

I can dream, can't I?:whistle:

And steady state? Guess I'm a bit averse to the losses in those?
 
guy's it is NOT the inrush current tht is the problem.
it is physically breaking the load (Back EMF or Spike) that is eating the contacts.
Contactors use arc quenching - Almost All PLC relays - Including Zelio - are rated at 3 Amps RESISTIVE. CFS aa with most AC lighting is INDUCTIVE.
Interposing rrelays is your only choice.
Also confirm the material of the contacts - Gold Plated are for DC loads Only
 
remember the Contacts of the Points in the old car HT distribution system.
the pitting would cause the points to stick and the car would run like a snail
 

Similar Topics

Good afternoon colleagues, a pleasure to greet you. In this opportunity I require some help from you. I am trying to make a shift register in...
Replies
2
Views
2,226
I have a zelio logic 2 smart relay on an alarm system. The relay is getting no inputs at all yet is showing the coil to be energised and the...
Replies
1
Views
2,526
Hi, I'm new to the site and was looking for some help with Zelio ladder logic. I'm an electrical apprentice and am currently in training and my...
Replies
4
Views
1,282
Hi There, I want to use a Zelio to monitor pulses coming from a device. If the pulses are higher than 0.5Hz, then the output is on but if it drops...
Replies
3
Views
1,902
I want to be able to pause a zelio smart relay timer, so when the machine is running the timer times, then pauses when the machine is stopped then...
Replies
3
Views
2,625
Back
Top Bottom