What is a "PLC-5 Crash log"? Do you mean the Fault bits? If so, then here is how to clear them.
Clear Minor Fault
A minor fault indicates a status change (for informational purposes only) or that a problem occurred, but that the problem is not severe enough to halt the processor.
To clear a minor fault, reset individual bits on the status displays where the minor error bit is displayed. If you are unsure where the minor error bit is displayed examine the minor fault table.
Clear Major Fault
A major fault halts the processor. You have to clear a major fault before the processor can continue to run the current program.
Warning! When a processor faults, you must find and correct the underlying cause of the fault before attempting to clear the fault. If you do not find out what is causing the fault, the processor may behave unexpectedly.
Tip
Interrogate the status file when the processor faults to determine the cause of the error. A quick method to call the status file when the processor has faulted is to click the drop-down arrow to the right of the Operational mode listbox in the online bar. Then click Goto Error. You can clear the error from the status file.
After making sure that the condition that resulted in the error has been corrected, use either method below to clear a major fault:
1 From the Comms menu, click Clear Fault.
2 Click the Clear Major Errors button on the PLC-5 Status - Errors Tab.
Alternate Hardware Method
Turn the key switch on the PLC-5 processor from REM to PROG to RUN.
Rockwell Software Inc., 1997, 1998, 1999, 2000