I had a problem yesterday with a drive tripping, showing the code E04(MotorOvertemp Fault). Today the same motor is tripping with the code E19(PositionErrorFault). I run two identical side to the machine with no problems on the opposite side. Is this likely due to binding/ friction?
 
Could be a lot of things. I find that help working out the problem I get a trend with the motor torque, Speed and acceleration and Position Error, Position feedback.

Could be Zero speed hunting, Gear Binding, Stopping at a position where you are pushing against an end stop, ramp rates, ie lots of things.

Kinetics
To get the Torque and Position Error you must
1) Set Axis Properties -> Drive Motor -> Real time Axis information Attribute 1 or 2 to Torque Command OR Torque Feedback and the Other to Position Error

2) Also in the Motion Group Properties
Set Attribute Auto Tag Update to "Enabled"

Once you have the trend post a jpg for more help

Note: you can also monitor the "Motor Capacity" which i think is the thermal model for the motor as a %
 

Similar Topics

Hey all, First time poster looking for a little help. I have a Kinetix 6000 drive that I am capturing faults for in RSLogix but I need some help...
Replies
0
Views
970
Good Morning , I have a bank of Kinetix 6000 Drives that I'm getting faults on. I took notice in my ControlLogix , Controller Tags for the...
Replies
3
Views
3,755
Hello all, We have a new customer who had a large A-B servo motor rebuilt and after reinstalling it they are getting a fault on the Kinetix 6000...
Replies
2
Views
5,231
Good Afternoon , I have a strange problem with 2 banks of Kinetix 6000 servo drives . The machine is running along for about 10 minutes , and...
Replies
2
Views
4,082
Hi,Guys: we got issue with Kinetix6000 servo drive with E06 (HardOverTravel Fault), I saw "AS_Axis06.PhysicalAxisFault" showing 1 at monitor tag...