MSutton Member M Join Date Sep 2015 Location Birmingham Posts 5 Aug 26, 2016 #1 I want to connect a S7-315 cpu to an Omron CJ2M via Ethernet I/P and transfer mainly bit data ie. turn an Omron output on from the S7-315 or turn a s7 output on from the Omron. Is it possible?
I want to connect a S7-315 cpu to an Omron CJ2M via Ethernet I/P and transfer mainly bit data ie. turn an Omron output on from the S7-315 or turn a s7 output on from the Omron. Is it possible?
Pudden Member P Join Date Feb 2009 Location Halmstad Posts 179 Aug 26, 2016 #2 Hi MSutton, Ethernet/IP on a Siemens 300 PLC will be very tricky, if not impossible. You will probably need to use a gateway, such as: If the S7-315 has Profibus, http://www.anybus.com/support/support.asp?PID=165&ProdType=Anybus X-gateway If the S7-315 has Profinet, http://www.anybus.com/support/support.asp?PID=301&ProdType=Anybus X-gateway BR Patrick L
Hi MSutton, Ethernet/IP on a Siemens 300 PLC will be very tricky, if not impossible. You will probably need to use a gateway, such as: If the S7-315 has Profibus, http://www.anybus.com/support/support.asp?PID=165&ProdType=Anybus X-gateway If the S7-315 has Profinet, http://www.anybus.com/support/support.asp?PID=301&ProdType=Anybus X-gateway BR Patrick L
MSutton Member OP M Join Date Sep 2015 Location Birmingham Posts 5 Aug 26, 2016 #3 Thought that might be the case. Thanks