Hello friends
I have new project
Air compressor the company want to upgrade it to work with PLC and HMI
The compressor work with micro processor and the micro processor
Is damaged the problem in 2 solenoid open the air gate and if the solenoid coil is broken the micro processor stop the machine and make alarm
The solenoid coil is normal only 2 wire 24v dc
How the micro processor feel the broken coil and if the wire is cut
And the owner need in the upgrade this feature
How can I make the plc feel the coil if broken or damaged
I will use plc s7 200 with out put relay
I think the micro processor measure the coil resistance
But in the plc ? what we will use ?
Sorry about my little English
And I am wait to answers me
Some PLCs manufacturers have output cards that will detect an open circuit on the output. I have only seen this feature with solid state outputs, never with relay outputs. The PLC output circuit applies a very low voltage limited current to the output terminal. This signal is not strong enough to activate a solenoid coil but it indicates to the controller if there is a completed circuit.
Wire the output as sinking. Wire an input directly to the output.
Input will be on when output is off, if the coil has continuity.
Input will be off when output is on.
You could also play the same trick with the input - have it high all the time , and the coil will pull it down . Touble is , that even if the coil fails , there is a chance that leakage alone will be enough to give spurious inputs . How about using a change over relay (actually not necessary) , and wacking a voltage over the coil with a ballast resistor (high impedance), you could then use an analogue voltage input to measure the voltage across the coil , which would change if the coil failed .
an alternate method would be to use a pressure switch tied to a timer. If in X time the pressure switch doesn't activate/deactivate...
dear Alaric
thank you very much can you tell me what the kind for this plc
and any mark and i see current sensing and leakage monitoring relay
its very good from you this is what i need but if i found the good plc will detect an open circuit on the output its will be the good idea i wait for your replay i need the plc manufacturers
and data sheet about it
dear keithkyll
i cant understand who is the input i have one solnied and need to feel it if the coil is damaged or broken the machine will stop
dear 10baseT
thank you for your help
dear stasis
big story to use pressure switch tied to a timer stasis another circle man
Output is relay. Solenoid has +24DC. Relay is controlling the zero side of the solenoid.
Think backwards. When the relay is off, +24 volts will pass through the solenoid coil to the relay contact. Connect a PLC input to this point.
I assume input is on with 24 DC input - off with zero.
If the PLC input has a 4ma load, then there will always be 4ma on the solenoid. This shouldn't be a problem, unless the solenoid is very small.
dear keithkyll
can you draw this steps for me
Wire the output normally. Add a jumper from the output terminal to an input terminal.
Someone help me out here with a drawing.
elhagen, think of using a meter to troubleshoot the output. Red lead on Output terminal, black lead on ground. When the output is on, meter will read zero volts. When the output is off, meter will read 24 volts if the solenoid is not open. If the solenoid is open, you will always read zero volts.
Use a PLC input as a meter.
Hello, I am a plc engineer and I have a job to do in the NIGERIA 25000 TON GRAIN SILOS STORAGE CONTROL PANEL. A problem where the panel is not...
27
The project on the operator workstation keeps disconnecting, even though I have an installation server and operating station set up through...
55
I have a problem, I'm running an AE Licence Manager on a Windows 2016 Server, and my Window Maker is on another separate Windows 2016 Server. My...
81
I have one old Ansaldo VFD from 37kW and it have only sign OFF on the display after put it on the 3x400VAC. Is there any idea, how to solve this...
81
23
616